Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Weil McCann GV90
Crissie
Member Posts: 132
This is a conventional cast iron boiler with a secondary stainless steel heat exchanger to allow for condensing and direct venting through PVC. Has anyone had experience with this, any feedback? Do you know if we would need to worry about boiler protection or supply water temp? Thx!!
0
Comments
-
-
I service a few of them.
That boiler has both an internal system circulator and an internal bypass circulator that mixes hot supply water with the return water when RWT drops to 140° to prevent condensing in the cast iron section.
I would pipe it (if more than one zone) primary/secondary as shown in the installation manual.
I've not had too many issues with them. The internal circulators are both Taco 007 unless newer revisions have different.1 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements