Weil McCann GV90
Crissie
Member Posts: 132
This is a conventional cast iron boiler with a secondary stainless steel heat exchanger to allow for condensing and direct venting through PVC. Has anyone had experience with this, any feedback? Do you know if we would need to worry about boiler protection or supply water temp? Thx!!
0
Comments
-
-
I service a few of them.
That boiler has both an internal system circulator and an internal bypass circulator that mixes hot supply water with the return water when RWT drops to 140° to prevent condensing in the cast iron section.
I would pipe it (if more than one zone) primary/secondary as shown in the installation manual.
I've not had too many issues with them. The internal circulators are both Taco 007 unless newer revisions have different.1 -