disk trap followed by bucket trap
pbraul
Member Posts: 2
Hi,
I run a small brewery and have noticed our installer put disk traps followed by bucket traps on all condensate returns. Is this a good idea? We have recently had issues with nearly all of the appliances and have only been running about 2 years. I have read this is double trapping and can cause issues and would consider removing the disk traps but feel a bit unqualified to make that call. Can you help?
I run a small brewery and have noticed our installer put disk traps followed by bucket traps on all condensate returns. Is this a good idea? We have recently had issues with nearly all of the appliances and have only been running about 2 years. I have read this is double trapping and can cause issues and would consider removing the disk traps but feel a bit unqualified to make that call. Can you help?
0
Comments
-
The disk trap, is that what you normally call a thermodynamic steam trap.
These traps are generally used on high pressure steam operations. Their capacity to drain condensate depends on the differential pressure between the inlet and outlet pressure at the trap. Example (inlet pressure 100 psi-outlet pressure 20 psig) the differential is 80 psig. When looking at the trap sizing capacity table you look at the 80 psi not 100.
Typically I would go for the bucket trap and no disk trap. TD traps work by the differential in temperature
between the top of the **** and the bottom of the disk while a bucket trap operates on a float. The float will adjust o the volume of condensate flowing though the pipe whether a large amount or small amount of water quietly, while a disk trap will be clicking and clicking.
Jake
Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron1 -
Thanks Jake, that is very helpful. We are running low pressure steam so if it's safe I think our first step will be to remove all of the TD traps and fingers crossed our processes all improve! Cheers,
Peter0 -
Agree with Jake0
-
It is it is never a good idea to double trap a condensate return line. Condensate will back up.Retired and loving it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements