MM-2 Mastertrol and wiring Sensi Wifi touch thermostat to Zone 2
Comments
-
it seems the Y (T6 on control board) carries power wondering if can swap Y and R at the thermostat connection???0
-
MM-2 control board? Can you post equipment wiring diagram and any zone panels or relays involved?
There should only be 24v at Y if its switched through the thermostat.0 -
-
talking about only zone 20
-
That's an obsolete Master/Slave damper control panel. Time for an upgrade.0
-
The slave stat is switching the common side, not the hot side. I'd suggest using the Sensi to switch two relays & use those to interface with the Mastertrol. You can pick up 24 VAC on terminals 1 & 2 to power the stat.
BTW, there has been some success reported in swapping out the Mastertrol to a TrueZONE panel with the existing Mastertrol actuators, with some rewiring (see https://forum.heatinghelp.com/discussion/155421/wiring-honeywell-hz322-from-a-trol-a-temp-mastertrol-mark-v).
0 -
Can you post the setup for the isolation rely between master troll and sensi?
0 -
-
Hay @miotov…. I agree with @EBEBRATT-Ed and also with @HVACNUT from 4 years ago. Did you read the entire discussion?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 134 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements