Preparation/post procedure for geothermal zone valve replacement
moose4747
Member Posts: 4
Replacing the taco zone valve, hopefully just the innards looks straightforward. What is not clear is what other than shutting down power is needed to do before starting replacement. Is this not something a new to geothermal person should do? None of the videos I see say much about purging lines or pressurizing etc. but most are in regards to boilers.
0
Comments
-
This is on the water side I assume.
Yes, shut off the power.
There should be isolation valves on the inlet and outlet pipes so close them and drain so you can solder.
If it's an open loop system then no purging is necessary.
Closed loop you have to purge.0 -
@moose4747
It's the same as working on a boiler system. usually 12-15 psi. I am sure there is a drain valve or gauge port you can put a gauge on and find the pressure before you start working.
I assume there may be antifreeze in the system you may have to deal with that0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements