The wiring diagram above shows the current journey downstream from the transformer (upper left) to the TACOS & T-stats.Steamhead said:
Where does the 24-volt wire go from this transformer?TheStressMachine said:
Here is the transformerJakeCK said:Also those are just pictures of the zone valves. Anything of the transformer its self?
0 -
If you wire it this way, it will work. R on the transformer goes to the red wire. The polarity does not matter to the motor, the smart t-stat cares.TheStressMachine said:Thanks everybody for the feedback, here's an upgraded diagram with what I'm going to do
- Confirm with multi-meter that TR/L1 is indeed neutral.
- Reverse the wires to the T-Stats so that W energizes TH (and my brain doesn't break when I see white/red together).
- Upgrade my transformer to 60vac
- Connect my common wires to TR/L1 (probably right at the transformer terminal)
Also, I borrowed a multi-meter and realized I won't see negative when testing neutral vs hot because this is AC. I tested both terminals with one wire on something grounded and didn't get full voltage on either, but one of the terminals showed almost a volt while the other showed nothing, I assume almost a volt is my hot? Any other way to confirm hot vs neutral on 24 VAC?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 - Confirm with multi-meter that TR/L1 is indeed neutral.
-
Thanks everyone for your patience as I grasp these concepts and shake off concepts from other electrical areas that don't apply. I now have a better understanding. It sounds like either of my two most recent diagrams would work, I just need to decide how much I want to get into while the wife gives me "the look" cuz the hot water gets less and less hot the longer it takes me.
0 -
TheStressMachine said:
That diagram isn't correct.
Wouldn't be surprised if it's not technically correct, just trying to retrofit what I have (everything except the blue wire and T-stat reversal) without getting into too much trouble, but I agree with you that a fuse needs to be present in case I do get into trouble. Seems like your suggestion is essentially reversing the polarity in the system but the end effect of opening and closing of circuits to call on hardware should be the same? Is this diagram more in line with what you're thinking? (Dotted red just represents energized only when circuit closed)
Your new transformer will have R and C.
R will connect to TR on the zone valves and RH on the thermostats.
C will connect to TH/TR on the zone valves and C on the thermostats.
And something tells me you should wire in an inline 5a fuse, or get a transformer with a circuit breaker.0 -
Yes, that puts everything where it should be.HVACNUT said:TheStressMachine said:
Wouldn't be surprised if it's not technically correct, just trying to retrofit what I have (everything except the blue wire and T-stat reversal) without getting into too much trouble, but I agree with you that a fuse needs to be present in case I do get into trouble. Seems like your suggestion is essentially reversing the polarity in the system but the end effect of opening and closing of circuits to call on hardware should be the same?HVACNUT said:That diagram isn't correct.
Your new transformer will have R and C.
R will connect to TR on the zone valves and RH on the thermostats.
C will connect to TH/TR on the zone valves and C on the thermostats.
And something tells me you should wire in an inline 5a fuse, or get a transformer with a circuit breaker.
Is this diagram more in line with what you're thinking? (Dotted red just represents energized only when circuit closed)
The motor needs a common. It works the way it is wired now, you just need a common for the t-stat."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
-
JakeCK said:I just want to point out that if he has to buy a new transformer that he is already 1/4 of the way to a 3 zone valve controller. And he'd get priority for his dhw and a bunch of fancy leds that tells him which zone is calling for heat. Just saying.
Much appreciated, now that I'm comfortable with how this all works it will be fun to look into the controller, I like the idea of setting priority and the status LEDs, and I'm certainly a gadget guy
0 -
Zman said:
The motor needs a common. It works the way it is wired now, you just need a common for the t-stat.TheStressMachine said:That diagram isn't correct.
Wouldn't be surprised if it's not technically correct, just trying to retrofit what I have (everything except the blue wire and T-stat reversal) without getting into too much trouble, but I agree with you that a fuse needs to be present in case I do get into trouble. Seems like your suggestion is essentially reversing the polarity in the system but the end effect of opening and closing of circuits to call on hardware should be the same? Is this diagram more in line with what you're thinking? (Dotted red just represents energized only when circuit closed)
Your new transformer will have R and C.
R will connect to TR on the zone valves and RH on the thermostats.
C will connect to TH/TR on the zone valves and C on the thermostats.
And something tells me you should wire in an inline 5a fuse, or get a transformer with a circuit breaker.0 -
TheStressMachine said:JakeCK said:I just want to point out that if he has to buy a new transformer that he is already 1/4 of the way to a 3 zone valve controller. And he'd get priority for his dhw and a bunch of fancy leds that tells him which zone is calling for heat. Just saying.
Much appreciated, now that I'm comfortable with how this all works it will be fun to look into the controller, I like the idea of setting priority and the status LEDs, and I'm certainly a gadget guy2 -
Thanks everyone for your patience as I grasp these concepts and shake off concepts from other electrical areas that don't apply. I now have a better understanding. It sounds like either of my two most recent diagrams would work, I just need to decide how much I want to get into while the wife gives me "the look" cuz the hot water gets less and less hot the longer it takes me.
This has been a great learning tool. Thanks for hanging in there @TheStressMachine!
BTW, I vote for using a zone valve control as well. Much easier to install and fantastic diagnostics.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements