Isolation Relay for ECM Circulator Pump

dneubauer09
dneubauer09 Member Posts: 15
edited August 2021 in Thermostats and Controls
Last winter I had a contractor install a new NTI vmax boiler.
Along with that, he installed a Grundfos Alpha2 CH circulator pump, as our old boiler and plumbing relied on the boilers internal circulator pump. The new pump is wired to the boiler's CH pump circuit, so it gets power only when the system goes on.

I was reading the install manual (page 57 in link below) for the boiler today and it states that if you use an ECM circulator pump, you need to use an isolation relay or you'll burn up the boilers control relay.

I am 99% sure the contractor didn't install a relay, as he didn't even install the pump until I insisted he needed to.

Now I'm at the point where winter is coming and I don't want to wear out my boiler, so this isolation relay needs to happen.

I've done automotive wiring plenty and I know what a relay is and how to wire one, but I haven't done this on an HVAC system before.

What relay will work for this purpose?

Thanks everyone!

Edited for clarity.
Link to manual:
https://ntiboilers.com/wp-content/uploads/2018/12/Vmax-Installation-and-Operation-Manual-pn-85171-1.pdf

Comments

  • GW
    GW Member Posts: 4,832
    Hopefully an NTI guy will chime in, but as a general heating guy, what you describe makes no sense. Maybe you mean additional circs? 
    Gary Wilson
    Wilson Services, Inc
    Northampton, MA
    gary@wilsonph.com
  • dneubauer09
    dneubauer09 Member Posts: 15
    GW said:
    Hopefully an NTI guy will chime in, but as a general heating guy, what you describe makes no sense. Maybe you mean additional circs? 
    See here, page 48, the CH pump.
    https://ntiboilers.com/wp-content/uploads/2018/12/Vmax-Installation-and-Operation-Manual-pn-85171-1.pdf

    Page 57 also has the notice about ECM CH pumps, which I'm pretty sure the Alpha is.

  • Zman
    Zman Member Posts: 7,611
    I am thinking that NTI has a design issue on the board that has issues with ECM's.
    One of these, or any relay with a 120volt coil would do the trick.
    https://www.supplyhouse.com/Tekmar-004-Relay-120-V-ac-coil-7924000-p?gclid=CjwKCAjwpMOIBhBAEiwAy5M6YFOj2Ix5DzxQQ2rrxVIgHs7TQAKgdGeLVeuUkx19iWLILB4v-481ZhoCn4gQAvD_BwE
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Dave H_2
    Dave H_2 Member Posts: 587
    I am not sure of the models of NTI boilers that need this but here is a simple relay that is used most often for circulators.

    So I have run into this before (check with NTI for more details) but ECM circulators have a higher in-rush current when starting (go figure since they are so energy efficient) and it has caused a safety relay on-board the controller to trip.

    The higher in-rush current is for starting purposes when a circulator is sitting for long periods of time. Their AC cousins have an on-board capacitor to take of it.

    I hope this helps, enjoy.

    Dave H.

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions

    Zman
  • hot_rod
    hot_rod Member Posts: 23,416
    Do you have zone valves? Is so the pump could be placed in auto adapt mode and plugged into a receptacle, powered constantly.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • dneubauer09
    dneubauer09 Member Posts: 15
    edited August 2021
    hot_rod said:

    Do you have zone valves? Is so the pump could be placed in auto adapt mode and plugged into a receptacle, powered constantly.

    Yes, I have zone valves, so that would probably work just fine.
    This is probably the easiest solution, actually.

    If I'm not mistaken, couldn't I just rewire the circulator pump from the CH pump circuit to the boiler's 120v line voltage input? That would eliminate needing another outlet and be minimal rewiring, since it is just moving the hot wire 3 terminals down.
  • dneubauer09
    dneubauer09 Member Posts: 15
    Dave H_2 said:

    I am not sure of the models of NTI boilers that need this but here is a simple relay that is used most often for circulators.

    This relay seems to have much more going on with it than I am expecting.

    I have 2 zones.

    Right now my thermostats are wired directly to the zone valves in parallel with the boiler to trigger it to turn on.
    Seems like with this, the thermostat would go to the relay, the relay would tell the boiler to turn on.
    Then the relay uses the 120v output of the boiler circulator pump circuit to trigger the relay to turn on the 120v to the ecm pump?

    Seems rather complicated and perhaps I need 2 zones, not 1?

  • mattmia2
    mattmia2 Member Posts: 10,958
    edited August 2021
    Just a RIB relay with 120vac coil 120vac contacts would do it for you. RIB is a brand of relays with flying leads designed to mount in a knockout, makes mounting and wiring simple.
    Zman
  • Zman
    Zman Member Posts: 7,611
    mattmia2 said:

    Just a RIB relay with 120vac coil 120vac contacts would do it for you. RIB is a brand of relays with flying leads designed to mount in a knockout, makes mounting and wiring simple.

    You probably want a relay with a 120-volt coil so the boiler will maintain control and DHW priority functions will be maintained.
    RIBs are great for your application.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Dave H_2
    Dave H_2 Member Posts: 587
    UPDATE - UPDATE - UPDATE

    Had a conversation with NTI engineering in regards to connecting ECM circs directly to the boiler controller.

    The recommendation (not to connect an ECM pump directly to the boiler) came from the circuit board that was used in our Tx, FTV and Vmax boiler series, which by the way are no longer in production.

    All other (including future) NTI product series allow for direct connection of ECM pumps to the boiler.

    If you are not sure which model you have, I would get in contact with NTI representatives and/or NTI directly.

    Enjoy

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions