Low suction pressure normal superheat
charliechicago
Member Posts: 131
Hello to all,
I am working on a ten year old residential split AC system with a TXV located in a finished basement that has worked fine until now. The system actually works fairly well even on hot days, its just 2-3 degrees off the thermostat setting. The suction pressure is 95 PSI, about 28 degrees, but the superheat is normal, at 10. The liquid line pressure is fine, the outside coil is clean and the subcooling is 10, which is what the manufacturer calls for. I changed the TXV but did not have any improvement. The only thing I can think of is a dirty evap coil. I just cant see that being the problem with a normal superheat and no icing of the coil.
Any suggestions would be appreciated.
Michael.
I am working on a ten year old residential split AC system with a TXV located in a finished basement that has worked fine until now. The system actually works fairly well even on hot days, its just 2-3 degrees off the thermostat setting. The suction pressure is 95 PSI, about 28 degrees, but the superheat is normal, at 10. The liquid line pressure is fine, the outside coil is clean and the subcooling is 10, which is what the manufacturer calls for. I changed the TXV but did not have any improvement. The only thing I can think of is a dirty evap coil. I just cant see that being the problem with a normal superheat and no icing of the coil.
Any suggestions would be appreciated.
Michael.
0
Comments
-
What is the airflow and what is the return air temperature? This sounds like low load. Cleanliness of coils and proper airflow should be confirmed before trying to diagnose the refrigeration sue of things.0
-
I assume this is a 410A system?
R22 that pressure would be on the warmer side.
Why did you change the TXV if the superheat is correct?
If it's not icing up perhaps your measurements are off? Is there any sign of frost at all on the evaporator?
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Although frost and Ice can occur any time the evap drops below 32 deg, with air moving across the evap you can usually get down to around 25 deg before icing up.
Sounds line a dirty evap, plugged filter, low air flow, dirty blower wheel etc.
Check supply and return temp and temperature split0 -
Thank you all for your responses.I don’t know the air flow measurements, I know you can’t properly diagnose without them, it’s being fixed and I just don’t have it. Having said that, the filter is clean, the blower is clean, and all the supply and return vents are open and not blocked and nothing has changed in the house that would effect air flow. The split is 19 degrees, it’s 410A and changing the TXV was a mistake.Thanks again.0
-
Your SH is fine because the x-valve is doing it’s job.Low air flow.What’s your Static pressures0
-
Bad capacitor or bad motor could change airflow along with people closing dampers...0
-
19° split? What's the problem?0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements