Adding 3rd zone /wiring question/ System 2000
KyleO
Member Posts: 48
in Oil Heating
So I'm adding a 3rd zone and have wired the Nest thermostat using 18/3. I could swear I have it right, Pics attached, but it keeps saying I don't have power to the thermostat. Any ideas out there? Thanks in advance.
R on T3 for power to trigger the zone, C on A2 for common (power to the thermostat), and W on A1. I'm sure I'm missing something obvious here.
R on T3 for power to trigger the zone, C on A2 for common (power to the thermostat), and W on A1. I'm sure I'm missing something obvious here.
0
Comments
-
-
Thanks HVACNUT, that seemed to solve the Nest issue. But even when I set the temperature above the current temp it doesn't kick the circulator on to actually pump hot water to the radiators. Any idea there? The circulator light goes on but it ain't pumping. Thanks again0
-
Pic attached. The zone valve does open, that's confirmed.0
-
0 -
Make sure I have this right here. You kick up the Nest and the zone valve opens, but the circulator doesn't pump? Zone valve end switch connected? Getting power?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:Make sure I have this right here. You kick up the Nest and the zone valve opens, but the circulator doesn't pump? Zone valve end switch connected? Getting power?
@KyleO, try the other heat zones. If they're operating normally then I'd say the new zone is air bound or there's a valve off.
If you dumped the whole system to install the new zone, everything might need to be purged. This would be a good time to check the Hy-Vent as well.
1 -
HVACNUT said:Jamie Hall said:Make sure I have this right here. You kick up the Nest and the zone valve opens, but the circulator doesn't pump? Zone valve end switch connected? Getting power?
@KyleO, try the other heat zones. If they're operating normally then I'd say the new zone is air bound or there's a valve off.
If you dumped the whole system to install the new zone, everything might need to be purged. This would be a good time to check the Hy-Vent as well.
The other zones work fine. I have power. Yes my zone valves use 2 wire and all are hooked up correctly. The 3rd zone valve does open when the boiler heats up and calls the circulator. But the output doesn't come. You're right the zone valve doesn't open right away until it's hot, which is quick.
I did NOT dump the whole system to hook up the 3rd zone, as I had shut offs for the output and the return, so I cut the caps, soldered on the new pipe and then opened up the shut off valves. I don't have any radiator vents in the whole house. I did slightly open the main vent valve (pictured). Is that the Hy-Vent you referred to?
How do I fix being "air bound"?
Thanks again
0 -
Turn off power.
Manually open the zone 3 zone valve and lock it open.
Make sure the boiler feed valve is open.
Close the ball valve on the return. It might be behind the Manager. Connect a hose to the drain valve on the return. Put the other end into a bucket or drain.
Open the drain valve and purge until its steady water.
Close the drain valve.
Open the ball valve.
Release the lever on the zone valve so it closes.
Turn power back on and see what you've got.
3 -
Great suggestion, @HVACNUT - there has to be a reason that there is no flow through that particular zone and being air bound would be a highly likely cause based on @KyleO ‘s description so far.For reference, when the circulator light is on, there is line voltage power to the burner and the circulator (through the burner/circulator relay). This means that the burner cannot fire unless there is power on to the circulator at the same time.The burner light indicates that T-T is closed on the primary control.Best,
RogerPresident
Energy Kinetics, Inc.-1 -
OK, sorry for the delay, got tied up on another job.
I followed @HVACNUT suggestions, got a steady flow, booted back up, turned on thermostat, boiler heated, circulator light turned on, zone 3 light turned on, zone valve opened, but I'm not getting heated water to actually pump thru the new lines.
Other zones work just fine still.
Help! What's next oh gurus of heat? Thanks guys0 -
Is this loop buried in a slab or crawlspace?
If your purging correctly and getting good flow, it should be circulating.
Does the zone split into 2 or more branches?
All valves are definitely open?0 -
What does the radiation of this new zone consist of? Head loss?KyleO said:OK, sorry for the delay, got tied up on another job.
I followed @HVACNUT suggestions, got a steady flow, booted back up, turned on thermostat, boiler heated, circulator light turned on, zone 3 light turned on, zone valve opened, but I'm not getting heated water to actually pump thru the new lines.
Other zones work just fine still.
Help! What's next oh gurus of heat? Thanks guysTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
HVACNUT said:Is this loop buried in a slab or crawlspace?
If your purging correctly and getting good flow, it should be circulating.
Does the zone split into 2 or more branches?
All valves are definitely open?
When I did the purge, I got lots of air then good flow, ran about 3 gallons into a bucket.
I know the zone valve works, during the purge, because when the drain valve was open (with the ball valve closed), the only way water would come out was when I had the zone valve manually open (held with my finger).
The only other valve is the ball valve above the zone valve and that's definitely open (same validation during the purge).
Im stumped...1 -
3 gallons is nothing. Purge like it owes you money. Let it flow and try to maintain 12 psi while doing it. You should be able to manually operate the automatic water feed valve. Don't go over 20 psi and 30 psi will blow the relief valve.
Turn down the temp or disconnect one thermostat wire from the water heater so its doesn't operate while purging.0 -
OK will do. I turned off the power on the last purge so it wasn't hot. Pressure is around 15psi. I'll report back, going to get a longer hose so I can avoid using a bucket and go into a drain.... Thanks again0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements