Chimney liner?
davey73
Member Posts: 9
I currently have gravity steam with a oil fired Burnham boiler. I’m considering installing a gas fired boiler to replace my old oil fired boiler. The old one is leaking water. Do I need to add a chimney liner for the new gas fired boiler?
0
Comments
-
Most likely you do need a liner. Weather you do or not depends on your location and other factors
Colder climate usually requires one.
Outside chimney usually requires one.
Also depends on BTU input of boiler and size of the existing chimney flue.
So there are a few factors involved.
Need more information3 -
All chimneys must be lined and must be suitable for the class of service. When you change fuels, NFPA 211 calls for a level II inspection, which will undoubtedly call for a liner sized to the new appliance. Note you'll need a stainless steel liner. Aluminum is approved for CAT I gas but only if that flue has not served oil or coal.2
-
Bob Harper as always is correct!
0 -
"Bob is brilliant. Side note - No matter what a liner should always be stainless or it will rot out fairly quick.0
-
LOL. Ok Tim and Jim--I owe you both a chicken dinner. Aluminum liners and B-vent were developed back when appliances were much lower efficiencies and have draft hoods. An 80% furnace will eat them up even if a draft hood equipped water heater is common vented adding a little dilution air. A side benefit is that ss conducts heat about 1/3rd as fast as aluminum. This means a comparable venting system in SS will generally have a higher stack temp., which leads to a stronger draft pressure at a given input rate and dilution air. Everyone has been trained like seals to use B-vent for connectors to push the charts for venting. This is all based upon empirical calculations- not actual measurements. It's all theoretical. What they haven't shown you is that using L-vent with its 400 series high nickel ss inner liner will keep stack temps up, minimizing stack losses, last longer and is rated for 20 degrees F higher than B-vent. This is appropriate because FVIR water heaters can run with a stack temp well above the 570F rating of L vent. L vent lasts longer, too.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements