No cool
Scottmanatee
Member Posts: 1
Insufficient cool. ambient 80°, wet bulb 72, dry bulb 66, superheat 18° sub cool 9 approach 7, amp draw low, return 73 supply 64, 145/300. 410 A
0
Comments
-
Your amp draw is low which suggests a damaged compressor that is not pumping like the compressor is 1/2 working.0 -
What about noncondensibles? shouldn't the high side pressure be about 250 with an ambient of 80? or maybe a bad cap on the condenser fan so it isn't running at full speed
edit:
er i only partially read a post on checking for noncondensibles. not really sure what the high side pressure should be.
Well, not sure here but i'm not ready to condemn the compressor yet.0 -
Make
model
a little history helps also.0