Capping off unused vertical steam radiator riser

branimal
branimal Member Posts: 233
I have a vertical steam riser pipe that isn't going to be used in the new configuration of my renovation. Initially I was just going to cap it off. The exposed portion of the pipe would clear the finished floor enough so that a cap could be adequately threaded on.

But I needed to shim up the floor in that area. So now the cap can only get about 3/8" of thread on.

I'm thinking I'll put a coupling on and plug the pipe. Just wanted to get a 2nd pair of eyes on this before I proceed.

This is a laundry closet.

Thanks.




Comments

  • Steamhead
    Steamhead Member Posts: 17,748
    That should work fine. Put the coupling on before you raise the floor.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting