problem replacing circ isolation valve that has check valve built in
Nom_Deplume
Member Posts: 91
Hello...the relevant part of our hot water heat setup (arrows indicate water flow direction) is
boiler --> isolation valve ---> circ --->isolation valve with check valve -->to radiators upstairs
The check valve started chattering some months ago and I asked about it here. I want to replace the valve marked in bold above.
These are standard flange valves, sold in pairs by Bell&Gossett/Check-Trol and others. See e.g. this link. There is no built-in way to prop the check valve open.
So the problem is that the water to the right of the diagram, up to the radiators, has no way to drain out. I can drain the radiators themselves through the return path, but there's water upstream of the valve and so I cannot unsolder it!
Is there a trick to this? Many thanks,
PS I stuck my finger into the check valve for a sec (detached from the circ of course) and water spewed all over the wall, electrical wiring, etc. Because of the actual layout there is no good way to collect the water.
boiler --> isolation valve ---> circ --->isolation valve with check valve -->to radiators upstairs
The check valve started chattering some months ago and I asked about it here. I want to replace the valve marked in bold above.
These are standard flange valves, sold in pairs by Bell&Gossett/Check-Trol and others. See e.g. this link. There is no built-in way to prop the check valve open.
So the problem is that the water to the right of the diagram, up to the radiators, has no way to drain out. I can drain the radiators themselves through the return path, but there's water upstream of the valve and so I cannot unsolder it!
Is there a trick to this? Many thanks,
PS I stuck my finger into the check valve for a sec (detached from the circ of course) and water spewed all over the wall, electrical wiring, etc. Because of the actual layout there is no good way to collect the water.
0
Comments
-
You could use your finger and a wet vac.0
-
You can hook up a pump to the return and unbolt the check flange and pump out the supply . I would recommend cutting one side of the pipe of what you are trying to unsolder .
There was an error rendering this rich post.
0 -
I have places a bucket below the fitting I am removing, set up a pump to pump out the bucket, loosen the fitting until it starts to drip, Then carefully allow the fitting to drain into the bucket with the pump operating. depending on how much water is being held up by the check valve, this could take some time. Use your hand to act as a valve to throttle the flow into the bucket to match the pump capacity.
Mr. Ed.
P.S. Sounds like you are getting wet on this one!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
OK, thanks everyone for confirming that there is no simple trick. The tangle of pipes and electrical wiring in the area made things difficult. I drained it, but yes, I got very wet on this one.
I considered putting a drain valve upstream, but finally didn't do it...this problem doesn't happen often. The valve with the chattering problem had been installed 16 years ago.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements