Best way to install a device (propress) in an immobile pipe?
sunlight33
sunlight33 Member Posts: 378
edited April 2021 in THE MAIN WALL
To install a device (like a dirtmag) with press connection on a 1'' straight pipe and the pipe happens to be immobile after cutting, is inserting a short piece of pipe into each end of the press then use no-stop coupling the only way?
    EBEBRATT-Ed Member Posts: 20,566
    If you absolutely can.t spread the pipe apart then yes. Either slip couplings or unions around the filter are better but cost $$
    kcoppIntplm.
    hot_rod Member Posts: 27,911
    The Caleffi NA 5453 has press union connections, very simple to add in .
    NA 545366 press, 545356 with iso valves.. It can be used on a vertical or horizontal line also.
    mattmia2 Member Posts: 17,584
    Not many situations where you can't undo a pump flange or some hangers or both to get the 3/4" or so to slip the fittings together.
  • sunlight33
    For my case it's either between the DHW tank and an elbow against the wall, or inlet of a LLH and an elbow against the wall. I can probably cut the elbow and rebuild from there but prefer something simpler.
    I notice for the Viega union fitting, the part where the two are mated, one goes inside of another by about 1/8'', so should I screw down everything and use that as a guide to cut the pipe? (or leave 1/8'' of wiggle room?)
    here is an example
    sunlight33
    pecmsg Member Posts: 7,325
    Slip Coupling
    or
    2