metallic noise from circ area and from baseboard
Nom_Deplume
Member Posts: 91
Hello...our hot water heating system has developed a faint but increasing "tinkling" metallic noise from some of the baseboards. The same noise can be heard at the circulator that drives these baseboards. In a stupid homeowner move, I replaced the circ (I had an extra one). It made no difference.
However if I turn the circ off while leaving the other circs on, the noise stops.
(a) Is the next possible culprit the check valve that I know is built into one of the isolation valves?
(b) How does one tell which valve has the built-in check valve?
(c) Why do I need a check valve at all? Our primary/secondary system has three circulators, i.e. two zones. The zones are so well-matched that I use one stat for both zones, with no over/under-heating. In other words the primary circ and two secondary circs all run at the same time. They run 12 or more hours a day (outdoor reset) for most of the season. No DHW. So why do I care about ghost flow?
Thank you!
However if I turn the circ off while leaving the other circs on, the noise stops.
(a) Is the next possible culprit the check valve that I know is built into one of the isolation valves?
(b) How does one tell which valve has the built-in check valve?
(c) Why do I need a check valve at all? Our primary/secondary system has three circulators, i.e. two zones. The zones are so well-matched that I use one stat for both zones, with no over/under-heating. In other words the primary circ and two secondary circs all run at the same time. They run 12 or more hours a day (outdoor reset) for most of the season. No DHW. So why do I care about ghost flow?
Thank you!
0
Comments
-
Possibly a small amount of air in the system. Check the pressure and the expansion tank and any air removal device.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks for the suggestion!
There is a Honeywell Supervent, but it is on the primary, and the noise is in a secondary (no noise if I run everything except this one secondary circ).
I have drained lots of water from the baseboards and do not know what else could be done to remove air.0 -
If you drained water from the baseboards and didn't keep the pressure up while you were doing it, you may have introduced air. It's possible that -- eventually -- the Supervent will do the job, but you may have to actually purge the loop.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Homeowner, but not so ignorant as to drain without leaving the fill valve open.
PS I figured out the answer to my question (b)---one valve has a longer body than the other, and it must be the one with the built-in check valve.0 -
introducing fresh water in to the system will introduce the air dissolved in that water so the air elimination will need to remove that air.0
-
-
Just an update. Of course it was not air making the metallic noise. The check valves built into pump isolation valves do not have any built-in way to lock them open. I jammed the check valve open with a small pellet made of aluminum foil. Noise is gone. I realize the foil pellet is slightly blocking the flow. I will change the entire shutoff/check valve during the summer.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements