Questions on ODR and Navien boiler on/off logic
My old boiler was set to 140 deg I believe and I never did have issues (I have pex in concrete and insulated (Unsure of R value) pex under stone floor.
Including the default ODR curves below.
Thanks much guys,
Dave
Comments
-
Any input/opinions?0
-
The default curves are exactly that. Defaults. If you happen to have a house and system which matches the assumptions in one of the default curves, wonderful. Doesn't happen often. The solution is to tweak the ODR curve to match what you need.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
that i understand, given the curves are going to be linear no matter what I do and the fact i'm not satisfying the slab sensor in colder weather w/ the current boiler off setup i wanted to increase it but was hoping someone else had some input on the repercussions of doing this. Or perhaps someone who has done just this.Jamie Hall said:The default curves are exactly that. Defaults. If you happen to have a house and system which matches the assumptions in one of the default curves, wonderful. Doesn't happen often. The solution is to tweak the ODR curve to match what you need.
Thanks
Dave0 -
The primary repercussion is that when you get it right it will be a lot more comfortable... and the whole system will work better. It's done all the time, and is part of the process of setting up the ODR to control your system. The on/off differential has noting to do with it. What needs to happen is that the slope and end points of the ODR curve need to be adjusted.
The procedure is buried in the manual and the menus. You might try low mass radiant instead of your present high mass radiant for starters, and work from there.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you for that. I'm not very educated in these things and don't want to just go making changes without considering the downfalls.Jamie Hall said:The primary repercussion is that when you get it right it will be a lot more comfortable... and the whole system will work better. It's done all the time, and is part of the process of setting up the ODR to control your system. The on/off differential has noting to do with it. What needs to happen is that the slope and end points of the ODR curve need to be adjusted.
The procedure is buried in the manual and the menus. You might try low mass radiant instead of your present high mass radiant for starters, and work from there.
Dave0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements