Dunkirk VLT Heat Exchanger Rumbling
JoeMagrino
Member Posts: 1
We had a Dunkirk VLT boiler with indirect water heater installed about 6 years ago. This morning we woke up to some rumbling in the basement. The boiler runs fine during domestic heating in low power, but as soon as central heating kicks in, the rumbling starts while in ignition power and high power. High power only lasts for about 10 seconds before powering down and recycling again and again. There are no failure errors on the screen. I tested the CH pump in low power, ignition power and high power. The only thing I can think of is scale. Is there anything else that can be wrong? Any other troubleshooting I can do? Thanks!
0
Comments
-
Yes, scaled HX surfaces can create that type of noise. It is usually a gradual build up and noise. Good news is that it is fairly easy to add a cleaner, flush and add good quality water. Efficiency should bump up also. Make sure the circulator is running during any boiler call.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Shouldn't a domestic call set the boiler to high fire?
When was the last maintenance done? Is there a copy of the combustion report?
Just because there's no error code and it hasn't gone into lockout doesn't mean there's proper combustion.0
Categories
- 113.3K All Categories
- 81.3K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 37 Biomass
- 394 Carbon Monoxide Awareness
- 2.7K Controls
- 1.4K Domestic Hot Water
- 3.9K Gas Heating
- 101 Geothermal
- 135 Indoor-Air Quality
- 2.4K Oil Heating
- 33 Pipe Deterioration
- 589 Plumbing
- 4.4K Radiant Heating
- 335 Solar
- 12.4K Strictly Steam
- 40 Water Quality
- 19 Industry Classes
- 54 Job Opportunities
- 8 Recall Announcements