Middle cast iron rad poor heat output

kensheets2
kensheets2 Member Posts: 36
edited March 2021 in Radiant Heating
Recently I installed a hydronic system using recycled cast iron rads.  I used two pipe reverse return with 5 rads.
The problem child is the middle unit there are two upstream and two downstream of this rad and all except for the middle heat up nicely, top to bottom.
I have TRV on all with a turn valve on the returns.  Bled all rads, even replaced trv and video scoped inside of bottom channel and all is well there.
TRV is hot to the touch return valve is warm at best.
 I would say the rad itself is about 2/3 or possibly 1/2 as hot as others.  I have all rad valves opened all the way.
Is this still a balancing problem perhaps?



Comments

  • neilc
    neilc Member Posts: 2,855
    edited March 2021
    is it possible the pex is kinked somewhere on that rad?
    how much of it can you see? back to your mains , , ,
    known to beat dead horses
    kensheets2
  • kensheets2
    kensheets2 Member Posts: 36
    Not likely, down stream rads working great
  • neilc
    neilc Member Posts: 2,855
    I'm referring to the short risers being kinked between the bad rad and the supply and return mains, not the mains themselves, ( or a blockage? )
    or are you saying you home run to manifolds?
    that rad has all the air out?
    known to beat dead horses
    kensheets2
  • neilc
    neilc Member Posts: 2,855
    Or,
    try this,
    since you have those TRVs,
    shut all of them but the bad rad,
    heat now?
    known to beat dead horses
    kensheets2
  • Ironman
    Ironman Member Posts: 7,555
    Are these five rads and their piping something that's been added to an existing system or are they the total extent of the system?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    kensheets2
  • mattmia2
    mattmia2 Member Posts: 10,955
    Are all the radiators the same? Are you sure that is a radiator where the top sections are connected?
    kensheets2
  • mattmia2
    mattmia2 Member Posts: 10,955
    I had to think about this a while, but the middle radiator is the worst case flow, especially if the piping to the radiators can provide more flow than is needed. The radiators close to the supply have more pressure from the circulator although the have little suction on the return, the radiators near the return have more suction on the return but little pressure on the supply. The greater pressure/suction at the ends means that the end radiators will get more flow if there is no restriction to even it out. I think what you need to do is close down the radiator valves progressively from the ends toward the middle to balance the flow in the system.
    kensheets2
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    Is the problem radiator heating at the bottom and not the top, or is it heating the first sections fully top and bottom?

    I ask this because systems that ran on gravity (before circulators showed up) connected bottom-and-bottom, as you have now. The slow gravity flow allowed the entering water to rise to the top of the radiator, displacing the cold water, which then fell out the outlet.

    Add a circulator to those jobs and the pumped flow now scoots directly across the radiator's lower push nipples. The bottom gets hot; the top stays cold. The classic solution to this problem is to throttle the valve at that radiator. The flow slows to a trickle and begins to mimic what went on in the days before circulators.
    Retired and loving it.
    kensheets2
  • mattmia2
    mattmia2 Member Posts: 10,955
    Now that i think about this more, i cant decide of the distribution balances out at each radiator or not.

    I think this is a new install so it doesn't have oversized mains like a gravity conversion would.

    I think this is the physical manifestation of this post:
    https://forum.heatinghelp.com/discussion/166481/single-pipe-or-2-pipe#latest
  • kensheets2
    kensheets2 Member Posts: 36
    edited March 2021
    Hello
    The system is piped with 3/4 pex and plastic fittings, about 100ft for supply and same for return.  Circs are grundfos ups15-58FC 1/25HP MAX 19.5 head.

    Mattmia2, I will try ur idea.  Dan Holohan, the problem rad, when warm heats top but bottom much cooler.

    The part that confuses me is the TRV is blazing hot but the return side is barely warm.  All other rads u can only touch for about 5 secs before u have to take ur hand away.
    What do u think of the circs?, i was really pushing the head I think.
    Forgot to mention if it makes any difference, I havent put the heads onto the TRVs yet so they are all full blast open as is the turn valves on the return.



  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,601
    Please put the heads on the TRVs. Let’s see what happens. 
    Retired and loving it.
  • kensheets2
    kensheets2 Member Posts: 36
    Dan, will do.