BTU output of 1 1/4 copper
charliechicago
Member Posts: 135
Hello to all,
I'm sizing a replacement STEAM boiler and wanted to know the BTU output of a 1 1/4 inch finned copper "radiator". Anyone know?
Thanks!
Michael.
I'm sizing a replacement STEAM boiler and wanted to know the BTU output of a 1 1/4 inch finned copper "radiator". Anyone know?
Thanks!
Michael.
0
Comments
-
How big are the fins? Spacing?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Not sure, will get back to you soon with info.
Thanks.0 -
Here is one brand that may get you close. Look at the ST 1200-3A at around 210° or somewhere between 210° and 220°
this is what it looks like. if your emitters are similar, then this will be close enough.
There are other configurations of 1-1/4 copper elements at this manufacturer web site
https://www.haydoncorp.com/catalog/category/commercial-baseboard
Yours truly,
Mr.Ed
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Thanks0
-
Some more information here:
https://www.slantfin.com/wp-content/uploads/2016/04/Fin-Tube-Selection-Guide-820.pdf8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Isn't knowing what sort of cabinet it is in and the pitch of the fins important here? So a picture would be good.0
-
I’ll get a picture too.0
-
The fins are 5 per square inch.
They are 3 by 3.5
0 -
You can come reasonably close to the EDR if you remember that EDR is actually a measure of the effective radiating surface area.
So... each fin has about 10.5 square inches on each side, or 21 square inches per fin, but you need to subtract the area of the hole for the pipe -- a bit less than 2 square inches. But then add the surface area of the pipe between fins. And call it 20 square inches per fin. And you have 5 fins per inch length of pipe (I think that's what you meant to say). So call it 100 square inches per inch, or 1200 square inches per foot of pipe. So... a very close approximation of the EDR would be 8 for each foot of finned pipe.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Wow, thanks.
So if I have 86 feet of this piping I come out with 165,120 BTU?
86 times 8 times 240.0 -
Looks about right -- always assuming that the air can circulate over those fins.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements