Can I control 2 circulator pumps with 1 thermostat
I have an old house with radiators throughout, there has been a 2 room addition put on years before I moved into it and they added a baseboard in each room and a thermostat back there to control a circulator just for those 2 baseboards, problem is it won’t turn on the boiler, only the main thermostat turns on the boiler, I’d like to get that circulator to run the same time as the main circulator which turns the boiler on. Right now I have a Beckett aquasmart control for the main thermostat/circulator which also controls the boiler and the other thermostat is hooked to a Honeywell Ra89a relay they just controls the circulator. Sometimes that circulator will run when the boiler is cold which is useless since it’s set up as a cold start, just trying to figure out how to get both circulators to run at the same time and eliminate the 2nd thermostat
  • SuperTech
    SuperTech Posts: 2,721
    If that is what you want to do you can just wire the 2nd circulator to the same terminals on the Aquasmart. You could also wire the thermostat to the same TT terminals on the Aquasmart as well if you don't want to get rid of the second thermostat. It's not the solution that I would go with. I think the best thing you can do is to get a circulator zone control board such as the Taco SR-503. This will allow you to wire the thermostat and circulator to their own relays that will energize the circulator and switch on the boiler independent of the other zones.
    ZmanEdTheHeaterMan
  • Depends......
    Piping layout/design/control strategies and wiring will have to be considered.
  • The wiring guide for your aquastat shows how to do this. A wire between the ZR terminal in the aquastat and the power for your circulator should allow you to have two independent zones that each fire the boiler on a heat call.  If you are not experienced with electrical work call someone that is.
    ryan242
  • Do we know the piping layout...Two pumps could end up fighting each other.
    So by that you mean run a wire from the ZR terminal and wire nut in with the hot wire going to the Second circulator? I’ve done some electrical before but never on these aquastats or relays, thanks for your help
  • wcsek
    wcsek Posts: 1
    I have sort of the same situation. Did you solve this? I have a main zone, on thermostat, relay switch that powers a circulator. I have a 2nd small zone on its own pipe loop, on thermostat, relay switch that powers a 2nd circulator pump. Id like to run them both on the main thermostat. They both have independent pipe loops to the boiler and want them both to heat at the same time. Can I simply wire the thermostat connections to the relay switch, to the thermostat connections on the 2nd relay switch so they are both triggered by the main thermostat? Thanks
    You might get a better response if you started your own discussion.
    The short answer is YES. but that may not be the best answer.
    Take some pictures and start a new discussion. Pictures of the circulator pump and what kind of control operates the circulator pump. What is the model number of the thermostat that operates the circ. pump control. What is the main boiler control that turns on the main circ. pump and the burner
    then explain your particular issue. if it is exactly the same at this one then you can reference this discussion by saying. "I believe this si the same problem as this one https://forum.heatinghelp.com/discussion/183396/can-i-control-2-circulator-pumps-with-1-thermostat "
    But I find that you get better response with a current discussion, not one dated February 2021
  • Do they make a split thermostat with sensors to control two separate zones. Thermostat to be placed in basement and sensors in two different apartments in apartment building.
    Jamie Hall Posts: 27,996
    um… may I ask why not two thermostats, one for each zone (perhaps with remote sensors), rather than a single device with two independent inputs controlling two independent outputs?
    EBEBRATT-Ed Posts: 21,352
    edited October 4
    @jpatlantic you would be better off with two thermostats each with its own remote sensor.
    If your controlling line voltage loads with the thermostats, you would need 2 Honeywell RA89A relays os similar.