What difference does keeping one radiator off do in single pipe steam system?
bipbap
Member Posts: 196
We have a 3-story multifamily building with a single pipe steam system.
There has always been one big old 36” wide and 39” tall radiator in the front lobby. My Dad has kept it turned fully off for decades because he’s old school and says no sense heating the lobby, and he thinks it saves money to keep it off. It’s on its own riser as well.
There has always been one big old 36” wide and 39” tall radiator in the front lobby. My Dad has kept it turned fully off for decades because he’s old school and says no sense heating the lobby, and he thinks it saves money to keep it off. It’s on its own riser as well.
Does that make any sense?
Will it save any money to keep it off in the scheme of a 3-story building with about 20 other radiators working?
Would it have any impact to the greater system to turn it back on? I just don’t want to turn it back on and then something on the 3rd floor starts acting up.
Thanks for the advice.
Will it save any money to keep it off in the scheme of a 3-story building with about 20 other radiators working?
Would it have any impact to the greater system to turn it back on? I just don’t want to turn it back on and then something on the 3rd floor starts acting up.
Thanks for the advice.
0
Comments
-
The cost is probably negligible although I suppose it could be up to a 5% increase?
throw a small vent on it like a Maid o mist #4 and see what happens!
Does your system currently cycle on pressure?NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Yes it is a vaporstat set to keep it under 1lb.
5% is actually significant, since sometimes the winter gas bill can be as high as $800 a month.0 -
Wait sorry, the system cycles when the thermostat temperature gets under 68 degrees. Is that what you meant?0
-
I meant anytime. If you open that radiator, the cycling will be reduced somewhat. That’s why I asked.
the 5% was the roughest of estimates because you have 20 other radiators (of unknown size)NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
So if we don’t really need the heat in the hallway, then would you say it actually makes sense to just turn it off since it won’t affect the greater system to turn it off and it can only be costing some amount more to keep it on?
Could my Dad be right again....?0 -
Yes, he could be.—
Bburd0 -
https://www.ispot.tv/ad/wlFY/progressive-group-sessionbburd said:Yes, he could be.
0 -
What sort of control is on the system?
Is the thermostat sensing the hall radiator?—NBC0 -
No the thermostat is not sensing the hallway, it’s inside an apartment far from the hall.
0 -
Steam will get to the other radiators faster if that radiator is closed off which is directionally good UNLESS your boiler on cold days or recoveries is cycling on pressure (radiators are getting full of steam on longer cycles causing system pressure to rise reaching the set pressure cutout point of the vaporstat or pressuretrol). In that case having the radiator shut off would hasten the rise of pressure vs having it open causing you to operate at higher pressure longer which would eliminate any savings and add stress on the system. I have 2 of 13 radiators closed which is a bigger percentile but manage still to keep my pressure from ever exceeding a couple oz even on the coldest days by restriction of my cycle time to not exceed 30 minutes.0
-
If you want the lobby cold, he’s right.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Yeah a cold lobby doesn’t really affect anyone so if it saves some money and doesn’t mess with the system I guess we will keep it shut off.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements