Replacing steam boiler
Sanddy0908
Member Posts: 14
I need help choosing a new boiler, i have an old burham boiler it has a domestic hot water coil in it which is no longer need it because i have separate hot water heaters. Question is should the next boiler be the same size or should it be smaller BTU wise since im not getting a boiker with domestic water coil? Please help from tge experts
0
Comments
-
The domestic coil won't have anything to do with the sizing of the steam boiler. If you would like help with sizing we can walk you through that process fairly easily.
Steam boilers are sized to the radiation. So you would add up the size of all the radiators and come up with an EDR rating for the system, then that is compared directly to the nameplate rating on the boiler.
https://www.weil-mclain.com/sites/default/files/wm-boiler-replacement-guide.pdf
Start on page 9 in the above link. If you get stuck post back and we should be able to help you through.2 -
This is the Tag of my boiler would you recommend grabbing a boiler withb a D.O.E of 201 MBH or 151 MBH0
-
The calculations need to be done for the system size, can't properly size off of a boiler tag.3
-
-
Replacing a boiler with a boiler of the same size assumes that the boiler was sized correctly to begin with and that no radiators have been added, removed or resized. Most boilers end up oversized because, every time a replacement is installed, the installer goes by the size of the existing boiler but adds a little "to be on the safe side." My own boiler is undersized because an addition was built, so they had to add a few radiators, but they didn't install a bigger boiler. Later, when they replaced the boiler, they probably got a bigger one, "to be on the safe side." but it still isn't enough for the total radiation. The only way to get a boiler of the correct size for the installed radiation is to determine the EDR of every darned radiator and add it all up. You can go a little over, but you should never go under.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks everyone for the information Really appreciate it. You guys are amazing! Heading back out to confirm the exact size they were. Things are starting to make sense.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements