Triangle tube solo 60 noise when ignite
pShah33
Member Posts: 1
I installed Triangle Tube Solo 60 six year back and doing service each year. Few months back service technician fixed recall and since then I am hearing noise when it’s ignite the flame on display. Can anyone advise? Can you recommend Triangle Tube boiler good technician ?
What did they replace on recall?
Was combustion analysis done?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I believe the recall was just securing the flue and make-up air connections to the cabinet which should not have effected performance.
Agree with Zman: A combustion analysis is the first step.
Click on "Find A Contractor" at the top of the page.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
- 87.5K THE MAIN WALL
- 122 Chimneys & Flues
- 116 Geothermal
- 169 Indoor-Air Quality
- 15.9K Strictly Steam
- 57 Water Quality
