I have this boiler Olsen Quantum 95M 200 - can someone tell me what the code "A" is?

Comments

  • nicholas bonham-carter
    Options
    Have you looked on line for a manual?—NBC
    Kaiswash
  • Ironman
    Ironman Member Posts: 7,376
    Options
    "A" is a self check code when the control is powered up.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    Kaiswash
  • Kaiswash
    Kaiswash Member Posts: 1
    Options
    ok thank you!
  • Kaiswash
    Kaiswash Member Posts: 1
    Options
    Yes, I pulled one off and there was no "A" in the troubleshooting codes? But I got the meaning for the "A" code...thanks
  • Kaiswash
    Kaiswash Member Posts: 1
    Options
    Phoned a second plumbing company to help me, the code on the boiler read 9 b 26 - the aquastat, LCW and 3.5 was checked and still the boiler would not fire up.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    The manual says it's an external limit code.

    Do you have good flow through the boiler? Not air bound? Circulator i working?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Kaiswash
    Kaiswash Member Posts: 1
    Options
    yes circulation is good, I've had my boiler for years. I woke up this morning and it was off, so turned the power off and then reset it. however, prior to this the PSI was at zero, so I filled it to between 15-20. The code 9 b 26 appeared then I repeated to turn off the boiler and then reset. It started to go, temp was increasing ...I last checked it was at 104...then I came back downstairs and it was off again and this time it won't start up. Its going to be -52 tonight so I'm in a bit of a panic mode
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Try removing the LWCO probe and cleaning it. You'll have to isolate and partially drain the boiler. Make sure all of the air is purged when it's refilled.