I added riser vents and noticed something interesting
jhewings
Member Posts: 139
I have a 1-pipe system with about 920 sqft of radiation (not sure about the EDR of a ceiling mounted radiator). The building is 3 stories. I decided to vent the 4 risers with Gorton "D"s. I did this after hearing a lot of whistling of air through the radiator vents on the 3rd floor. I am hearing much less whistling now. The thing I find interesting is that within a few seconds of the Tstat ending the call for heat, one of the riser vents begins loud whistling which lasts for maybe 10 seconds. I held a match to the vent and air is going in. I suppose a vacuum is being created in the system and the air is rushing in?
0
Comments
-
There are 2 mains each with 2 Gorton #2s0
-
Whistling radiator vents usually points to under capacity of the main vents.—NBC0
-
I calculated the volume of the mains. 1.43 cuft and 1.75 cuft. I thought they were close enough in size to vent them equally. They each have 2 Gorton #2. The riser vents seem to be helping with the whistling.0
-
At the end of a call for heat, all the steam currently in the system will condense at basically the same time and will cause a reduction in pressure (vacuum) in the system that is relieved through one or more vents, as you are seeing.
It's typical that one vent cuts loose first and relieves most of the pressure imbalance. That vent will make some noise. Hopefully it's a main vent, or at least a vent not in your bedroom.NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
If my system runs for a long time, I'll often have the long whistle as the system sucks air in.
But it doesn't seem to happen as much with Gorton vents as it did with Hoffman.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements