Circulation pump running constantly
Beakster
Member Posts: 7
Hi,
Notice today that my house was too warm and yet I could hear the heating running.
It's multizone hydronic flooring heated by an electric boiler.
I looked at my zone valves and they were all closed, as they should have been. But I could feel and heat the pump running and it was very hot in the heating cupboard.
I checked the voltage to the pump and it was on, so i disconnected the neutral wire.
What could cause this? I am guessing a stuck relay in the control module? Is this likely to be repairable?
When the boiler has circulation does that mean it constantly heats? Is it safe to just disconnect the circulation pump power?
Thanks
Notice today that my house was too warm and yet I could hear the heating running.
It's multizone hydronic flooring heated by an electric boiler.
I looked at my zone valves and they were all closed, as they should have been. But I could feel and heat the pump running and it was very hot in the heating cupboard.
I checked the voltage to the pump and it was on, so i disconnected the neutral wire.
What could cause this? I am guessing a stuck relay in the control module? Is this likely to be repairable?
When the boiler has circulation does that mean it constantly heats? Is it safe to just disconnect the circulation pump power?
Thanks
0
Comments
-
Either a zone valve end switch is stuck closed or the circ relay. Disconnect the end switch leads from the relay, see if the circulator stops. A volt meter is helpful for troubleshooting🤓Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I wish you'd disconnected the hot lead instead of the neutral... I really wish you had...
If the boiler heating elements are off, it's not generating heat, and they should have turned off automatically if it had gotten too hot.
It may well be a welded relay, or it could be any number of other failures in the system. Without probing the board, it would be impossible to say. Is it repairable? Only maybe. Sometimes -- if you can find the faulty component -- it can be replaced.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Hi. Thanks for reply. I have a multimeter here. The relay is inside the control module so I'm not sure what I can do to diagnose it.
How would I diagnose a zone valve end switch? All the zone valves appear closed. Each zone valve is connected to the module with 4 wires.0 -
It's simple enough. Determine which two terminals on the zine valve are power, and which two are the end switch (note that some zone valves only have three terminals -- one is common). If the zone valve is closed, the end switch should show an open circuit (you may have to disconnect one terminal, depending on the rest of the wiring) If the zone valve is open the end switch will show a closed circuit.
Caution: find out if any of the terminals are live before you play, and if in doubt turn off the power.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements