I have a WM Aquabalance ModCon Series 1. It's pretty cold for here, 24 deg F.
My wife pointed me to a pile of ice forming below the exhaust of the modcon.
The boiler is on outdoor reset and is currently operating at 140 degrees supply with 120 degree return.
Therefore I expected the flue gases to condense inside the heat exchanger. I guess its possible for _some_ water to come out, but this seems like a lot.
I just cleaned out the sediment trap, and its dripping a bit now, but the condensate drain has no water coming out, and inspecting the drain line it seems somewhat dry.
Any thoughts on what could be going on?
My wife pointed me to a pile of ice forming below the exhaust of the modcon.
The boiler is on outdoor reset and is currently operating at 140 degrees supply with 120 degree return.
Therefore I expected the flue gases to condense inside the heat exchanger. I guess its possible for _some_ water to come out, but this seems like a lot.
I just cleaned out the sediment trap, and its dripping a bit now, but the condensate drain has no water coming out, and inspecting the drain line it seems somewhat dry.
Any thoughts on what could be going on?
0
Comments
-
Pretty normal. If you see a plume out of the exhaust that's water vapor. You are bound to get a bit of frozen condensate ...especially at -24.
0 -
Sorry, not -24 but "approximately 24 degrees"0
-
Completely normal at the -24F degrees. You going to have to keep an eye on that flue exhaust and keep it clear. Most of the condensate is supposed to drain back down the flue pipe toward the boiler and drain out the boiler drain. However when the exhaust gas cools enough more moisture will condense out of it. And at -24 it's really condensing.
Check to make sure the flue pipe is low on the boiler end.
Possibly insulating the flue pipe will help
0 -
Its 24 degrees, not -24 degrees,I used the symbol ~ or tilde to denote approximate, not negative.0
-
Is this a two pipe set up (vent and intake ) or the concentric combined set up?
0 -
Two pipe setup.0
-
Totally normal. Just make sure it doesn't dam. Assuming it's a horizontal flue, a tee with the run on the vertical and the exhaust in the bull will solve it. As is, the condensate at at the end of the exhaust isn't dropping off, but trailing back on the underside of the pipe. It needs a positive drop off.
0 -
does this mean the flue gases aren't condensing inside the heat exchanger? If the return temps were lower would this happen less? any temp at which it would stop?0
-
It happens in the HX and the flue most all the time. Unless you are running really high temps.
How long a run is this vent?
0 -
the vent is not too tall, maybe at most 2ft vertical and a foot horizontal.0
-
The flue gasses are condensing in the boiler -- up to a point. Then they keep on condensing as they cool further. Some of that condensate will be in the exhaust and will drip back in -- but some of it will still be condensing when it hits that 24 degree air.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Totally normal. I get quite the large icicle off of my exhaust vent from my 2006 installed Vitodens 200 during the winter. even 90F exhaust from your boiler will have humidity in it, which will condense and freeze in cold enough weather.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements