No flame

Dbon
Dbon Member Posts: 1
I have a boiler with a fenwal ignition module. HSI.  It locks out intermittently. I get 24v to valve and no flame. After 3 tries it locks out. Then an hour later it'll try again. Then it'll start working again. I don't know how often it locks out but when it's really cold out I'll notice it more.  As recommended I changed the gas valve but it still happens. Thanks for your help

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,482
    @Dbon
    sounds like a gas valve issue if you truly have 24 volts at the valve and it's not opening,. Check the outlet of the gas valve by putting a low pressure " of water column gage or a manometer on the gas valve outlet port or on the burner manifold see if your getting gas pressure.

    Also check and tighten all wiring connections
  • mattmia2
    mattmia2 Member Posts: 10,948
    Check the pressure on the inlet as well to make sure there isn't some other issue like a bad service regulator
  • mattmia2
    mattmia2 Member Posts: 10,948
    Is this propane or natural gas?
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,386
    Is the Hot Surface Ignitor an aftermarket replacement? I know that there is an American Standard furnace that does not ignite the gas with aftermarket ignitors. Must use OEM ignitor on that model. I wonder if you have a similar issue?

    Yours Truly,
    Mr.Ed

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?