No flame

Dbon
Member Posts: 1
in Gas Heating
I have a boiler with a fenwal ignition module. HSI. It locks out intermittently. I get 24v to valve and no flame. After 3 tries it locks out. Then an hour later it'll try again. Then it'll start working again. I don't know how often it locks out but when it's really cold out I'll notice it more. As recommended I changed the gas valve but it still happens. Thanks for your help
0
Comments
-
@Dbon
sounds like a gas valve issue if you truly have 24 volts at the valve and it's not opening,. Check the outlet of the gas valve by putting a low pressure " of water column gage or a manometer on the gas valve outlet port or on the burner manifold see if your getting gas pressure.
Also check and tighten all wiring connections0 -
Check the pressure on the inlet as well to make sure there isn't some other issue like a bad service regulator0
-
Is this propane or natural gas?0
-
Is the Hot Surface Ignitor an aftermarket replacement? I know that there is an American Standard furnace that does not ignite the gas with aftermarket ignitors. Must use OEM ignitor on that model. I wonder if you have a similar issue?
Yours Truly,
Mr.EdEdward Young Retired HVAC Contractor & HYDRONICIAN Services first oil burner at age 16 P/T trainer for EH-CC.org0
Categories
- 120.2K All Categories
- 83.6K THE MAIN WALL
- 2.8K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 414 Carbon Monoxide Awareness
- 30 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.6K Gas Heating
- 114 Geothermal
- 152 Indoor-Air Quality
- 2.9K Oil Heating
- 49 Pipe Deterioration
- 736 Plumbing
- 5.2K Radiant Heating
- 356 Solar
- 13.8K Strictly Steam
- 3K Thermostats and Controls
- 50 Water Quality
- 36 Industry Classes
- 69 Job Opportunities
- 14 Recall Announcements