Ultra 105 Series 3 Ignition Fault

Options
landrthegreat
landrthegreat Member Posts: 1
edited January 2021 in THE MAIN WALL
My Ultra Series 3 105 boiler keeps going out on ignition fault when there is little demand.  To get it fired back up I have to put my hand over the intake horn to choke it.  I have changed out the ignitor and cable and just had it annual cleaning.  As long as there is demand, the boiler keeps working with no issues, but as soon as it gets a bit warmer outside it goes off on ignition fault.  Any suggestions on how to adjust?  My local service guy is real nice, but does not seem to have a lot of understanding of these boilers.

Comments

  • Ironman
    Ironman Member Posts: 7,376
    Options
    Has been setup with a digital combustion analyzer? If so, what are the numbers?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    HVACNUT
  • HVACNUT
    HVACNUT Member Posts: 5,841
    Options
    Agree with ☝️. WM wants to see 9% CO2 high fire, 8.4% CO2 low fire, less than 60 PPM CO on either. 
    Nat gas lockup 5 in. minimum. 
    Without those numbers, we're throwing darts.