Vacuum Breakers
dyoung9121
Member Posts: 24
Is it normal to put vacuum breakers on the main steam line and on the steam header. Wouldn’t a main vent be a better option?
0
Comments
-
No and yes. But not on the header -- the main vents belong on the outer ends of the steam lines (one pipe and many two pipe) or on the dry returns (most vapour systems and some two pipe with crossover traps). They don't accomplish anything at the header.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Okay so I have a 2 pipe with crossover f&t’s. Half way down the steam main there is a vacuum breaker but it looks like there may have been a vent there originally. Then on the header there is also a vacuum breaker so I guess what I’m asking is can I swap those breakers for main vents?0
-
Yes you can -- but keep in mind that they won't speed up steam delivery to any part of the main downstream from them.
Are the crossover F&Ts working properly? They are very much not my preference for crossovers -- a thermostatic (like a radiator) and a water seal have much more venting capacity -- but it is what it is. Do you have plenty of venting on the dry returns at the boiler?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie, we just replaced all the f & t ‘s and there are plenty of old vents on the dry return but we are replacing them as well as all them are way over 10 years old0
-
-
Thanks for the responses. I am going to keep the breakers cause I was trying to find ways of speeding up the venting but I think I’ll do that with the main vent at the end of the steam main0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements