I am annoyed at the sound emitted from the circulator pumps that resonate throughout the zones. It's has a tone to it, not a whistle, like a medium pitched hum.

Comments

  • epmiller
    epmiller Member Posts: 28
    Just a WAG, but is the distribution piping mounted tightly to to joists or otherwise tight enough against the floor structure to easily transmit noise? I’ve seen pipes hung with rubber isolators inside the hangers although I didn’t experiment with removing some to see if it was doing much. I have to look up the pump curve of that B&G to see if another idea I have might help. 

    Is the boiler circulator a 3-speed? If so, slow it down one step and see what that does. If only one zone is calling for heat, that will take off less heat than if all zones are calling. If you slow the boiler circulator down it could affect how much heat is available when multiple zones are calling.
  • Ironman
    Ironman Member Posts: 7,551
    Whats the delta T on each zone? More than likely, you're over-pumping.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ChipDryden
    ChipDryden Member Posts: 17
    I've set the speed on (1) the lowest setting. I think at most 5 degrees delta T. It's a single story ranch house.
  • Ironman
    Ironman Member Posts: 7,551
    Velocity noise + low delta T = over-pumping. Chances are, you could get by with one secondary circulator and 4 zone valves instead of 4 pumps. We would have to know the details of the system to confirm that.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • fenkel
    fenkel Member Posts: 162
    To determine if your pumps are incorrectly :
    How many btu are in each zone?
    Next how long is each.zone in feet..
    Formulas to use:
    Each zone btus divided by 10000, will determine gpms for the zone.
    Next for same zone..
    Total feet of zone x1.5 and then x.04   (.04 is used with 3/4 copper pipe) this will determine zone head pressure
    Example.. zone uses 25000 btus and is 200 feet long
    Gpms = 2.5
    Head pressure = 12.0 psi of head pressure
    Use these two number to look at your pump curves for the pumps considered..
  • ChipDryden
    ChipDryden Member Posts: 17
    edited January 2022
    Thanks.

  • Robert_25
    Robert_25 Member Posts: 549
    Try throttling the flow with the ball valve on the output side of the circulator.
  • ChipDryden
    ChipDryden Member Posts: 17
    Thanks for chiming in. I tried that-It does dampen the tone somewhat but then creates a whooshing water sound at the valve. I was concerned that may damage the pump to I left the valve fully opened.
  • fenkel
    fenkel Member Posts: 162
    Are you using flow control values?
    Are the plastic ifc installed in pumps?

  • ChipDryden
    ChipDryden Member Posts: 17
    edited January 2022
    Thanks for the suggestions.