Low temps with Runtal UF radiators and efficiency
moral212
Member Posts: 7
i believe i am losing efficiency with my current heating setup (but maybe not?).
Setup:
IBC hc series boiler
1 zone of the house is on radiant under floor heating (wood floor staple up)
1 zone is using Runtal hydronic UF radiators
Controlled with a taco relay srp
Notes:
The temp curve is set lower due to the radiant.
Runtal UF states they can be used with low temp heating
The Runtal heaters may be a box undersized for the spaces at low temp.
Q’s-
Am i burning more fuel running the boiler at low temps for longer than say high temp for shorter?
How to alter the system to provide higher temps to the radiators without buying and installing lots of expensive and complicated components? Should I just raise the temp curve?
Setup:
IBC hc series boiler
1 zone of the house is on radiant under floor heating (wood floor staple up)
1 zone is using Runtal hydronic UF radiators
Controlled with a taco relay srp
Notes:
The temp curve is set lower due to the radiant.
Runtal UF states they can be used with low temp heating
The Runtal heaters may be a box undersized for the spaces at low temp.
Q’s-
Am i burning more fuel running the boiler at low temps for longer than say high temp for shorter?
How to alter the system to provide higher temps to the radiators without buying and installing lots of expensive and complicated components? Should I just raise the temp curve?
0
Comments
-
If the Runtals are giving you satisfactory heat, and the boiler is intended for low temperature operation (a mod/con), then no -- the lower temps for longer will give you better efficiency. However, if the Runtals are not giving you satisfactory heat, you'll have to raise the temperatures (the temperature curve) to accommodate them, and mix the boiler water down (which isn't that hard to do).Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Got it! Ok, thank you. Guess I am running efficiently then!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements