Banging riser

What would cause a riser to bang horribly in only one apartment in a 21 floor building?

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,493
    Indeed. A sag -- or badly pitched -- horizontal section somewhere along that particular riser. It could be in the basement -- but it also could be between floors somewhere. More likely the latter, if it is just one apartment.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 363
    If it's one pipe steam, somebody could have tried to modulate their heat with the valve too!