Options
corey_denver
Member Posts: 10
Maid-O-Mist #75 as one-pipe steam main vent? Does that sound right? I can't find much about them but it seems like they are for hot water systems.
0
Comments
-
You are right. It’s not for steam, it’s to eliminate air from a water system
Read about it here: https://www.supplyhouse.com/Jacobus-Maid-O-Mist-75-75-1-2-Auto-Vent
try a Maid o Mist #1 from the same placeNJ Steam Homeowner.