Radiators staying warm even when thermostat asks for no heat.

My next door neighbor had his 1950s boiler replaced in 2016 with two Buderus cast iron gas boilers (Model G234X-45/5) each with an input rating of 186,000 BTU/h and an output rating of 153,000 BTU/h. The house is about about 4,000 sq feet and had an original gravity hot water system installed in 1891.
My neighbor was saying that on mild days when the outside temperature is in the 50s and the thermostat is not asking for any heat, his radiators remain lukewarm, and the house gets too warm. He then has to go into the basement and switch both boilers off.
The boiler piping appears very "creative" to me. There is a circulator pump on the return, which is then split evenly into each boiler. The boiler supply pipes then join each other in a T and get connected to the old gravity supply pipes. I will include a photo.
I am no expert, but this looked wrong to me. I told my neighbor that I thought perhaps the boilers keep themselves somewhat warm even when no heat is demanded in order to minimize condensation upon a "cold" startup, and with this piping system, the warm water in the boiler gently rises out of the boilers and circulates through the old gravity system.
Have you all seen a two cast-iron boiler system piped this way or experienced warm radiators when no heat is required?
Here is a photo. The pipe coming in from the right side with the pump on it is the cold water return. The pipe coming off and heading to the floor goes to the compression tank. The pipe on top goes to the supply side of the system.

My neighbor was saying that on mild days when the outside temperature is in the 50s and the thermostat is not asking for any heat, his radiators remain lukewarm, and the house gets too warm. He then has to go into the basement and switch both boilers off.
The boiler piping appears very "creative" to me. There is a circulator pump on the return, which is then split evenly into each boiler. The boiler supply pipes then join each other in a T and get connected to the old gravity supply pipes. I will include a photo.
I am no expert, but this looked wrong to me. I told my neighbor that I thought perhaps the boilers keep themselves somewhat warm even when no heat is demanded in order to minimize condensation upon a "cold" startup, and with this piping system, the warm water in the boiler gently rises out of the boilers and circulates through the old gravity system.
Have you all seen a two cast-iron boiler system piped this way or experienced warm radiators when no heat is required?
Here is a photo. The pipe coming in from the right side with the pump on it is the cold water return. The pipe coming off and heading to the floor goes to the compression tank. The pipe on top goes to the supply side of the system.

0
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 567 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.2K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
On the radiators staying warm. The first question is... do the boilers run from time to time? If they do, there will be gravity circulation in that setup (that, after all, is what heated the place before, no?). Then the question is -- why do the boilers run? It may well be a cold start protection, and it may be very hard to get rid of the problem with that piping.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
https://www.pmengineer.com/articles/87639-multiple-boiler-systems
I wonder if the DHW uses an indirect tank?
Jamie, there are no powered valves or any separation between the two boilers. My neighbor was under the impression that the left boiler was primary and the boiler on the right secondary. While I was visiting, the right boiler turned on, and while we were watching, the left one turned on too. I don't know if it was because heat was demanded by the thermostat or the boilers were just keeping themselves warm. I put my hand on the circulator, but couldn't feel any vibrations, but with these new ones, I'm not sure that's a reliable way of telling whether or not it's running.
But with two boilers with no separation like that, they both have to be running to get any real heat at all -- the shortest path for the water (remember, the stuff is lazy) otherwise is out of one boiler and into the other, and around and around we go...
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch