Pressure + Temp gauge...and pig tail is still acting up
Hello All...
As some of you might have seen... I recently put a new pigtail, clean the pipes that connect to Pressuretrol and gauge...
Q1) it seems like I have to keep use the compressor to push air in to the pig tail (boiler) to get steam... at least at 1 psi there is not steam coming out of it unless each time I push air in to the boiler) What could it be doing that?
Q2) I would also like to replace the pressure gauge on the pig tail that give me both temp and pressure... but I do not know how hot residential steam can get. Attached is the one I am considering (it has max temp to be 225F... or should I look for pressure and Temp gauge that give higher temp .
Thank you!
LS123

As some of you might have seen... I recently put a new pigtail, clean the pipes that connect to Pressuretrol and gauge...
Q1) it seems like I have to keep use the compressor to push air in to the pig tail (boiler) to get steam... at least at 1 psi there is not steam coming out of it unless each time I push air in to the boiler) What could it be doing that?
Q2) I would also like to replace the pressure gauge on the pig tail that give me both temp and pressure... but I do not know how hot residential steam can get. Attached is the one I am considering (it has max temp to be 225F... or should I look for pressure and Temp gauge that give higher temp .
Thank you!
LS123

@LS123
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 562 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
There is no need for a temperature gauge on steam heat (unless you want it to check the performance of an indirect water heater). Steam will be between 212 F and 215 F. Pressure will -- hopefully -- be below 2 psi.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
any thoughts about why I have to keep blowing air in to the boiler to get steam out and in the the pig tail?
Before I put the new pigtail... I poked inside of the boiler for a long while with a metal stick thing... I am confused about it... At one point I flood the boiler until water come out of the pig tail... and the water comes out pretty fast.... Any thought..... anybody? Thank you!
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Note that if the tubing can't stand boiling water, it will get pretty floppy pretty quickly... be prepared!
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
@Jamie Hall thank u! i will try that out tomorrow morning/... I think I have 1/8 soft copper tubing in the garage... Thanks again for both of your responses!
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
* House get heated and no issues with that...
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Best!
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Someday you are going to get a real surprise.....I have blow down valves on strainers for F&T traps, I am always amazed how violent just 1.5 LBS of steam can be when it is really cooking.
That temp/pressure gauge you pictured above is worthless for steam. The pressure would not even budge the needle....look what it does for the 0-30 gauge. And temp is not needed, it is going to be 212-215 degrees depending upon the pressure and we all know it should be under 2 PSI.
And the water in the pigtail loop may hold back some steam but eventually it will push it up and onto you.
You can be burned badly.
Pay attention to what Fred said about the orientation of the pigtail loop. If wrong it will tip your HG P-trol off level when heated up.
And do you mean the boiler would run until the temp on the tstat was met??
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Steam Heat Enthusiast
-- In Learning Mode --
"Trust But Verify" <-- Suzanne Massie, an American scholar
*Always Safety First*
** Not Everything Is DIY**
***Quest For Knowledge Is Important ***
Just to conclude...
This is a resolved matter now... ... I had the incorrect understanding that Steam boiler should run until it hits what is set on the P-trol (max 1.5 PSI) , then shut the boiler (and continue to run steam until the boiler pressure returns to min setting... or temp setting on Tstat has met (like a water boiler with radiators and circulator... which reach max temp, burner shouts down and cycle water until it hit the min temp settings or tstat settings... then run the burner again if needed.
It is very clear that P-tro is for safety, Tstat is primary control for burner, until Tstat send a signal for boiler to shut down when temp setting has met. Pigtail, P-Trol, pressure gauge on it is on correct physical position and settings. Although old(really OLD) Front mounted 30 PSI states boiler is reaching about 1.5 PSI, on the Pig Tail new 3 PSI pressure gauge (certified for Steam boilers) indicate far less pressure build up ( like less than 1/2 pound of pressure.)
To clarify Burner runs more than 3 or 4 times during 24 hour period. My observations is burner runs about 30 or 40 (+ or - 10) minutes to bring radiators to be hot enough ( I mean really HOT) to meet the Tstat settings.
Since the two main vents has been replaced with Gorton #2 yesterday evening, I am confident the boiler, main pipes are at best settings, and performance of the system will only get better...
Thank you all for all the helpful information.