Boiler cycle every minute or 2

Hello , my boiler was installed about 3 years ago and now I notice it going on and off. After the first cycle I notice that it shuts off on low water. When it comes on again it will run for 1 minute and I can see all the water going down on the glass very fast and it goes below the cut off point. The boiler shuts off and again I watch the water comes back up within 1 minute and it fires again. After 1 minute it does it all over again and again. I drained my boiler once a month. Pressurettol is set to about 2 psi. It is not going off on pressure. I need help. Thank you
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 129 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 560 Plumbing
- 4.2K Radiant Heating
- 332 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
Wilson Services, Inc
Northampton, MA
www.wilsonph.com
[email protected]
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
what's the boiler pressure on the gage while it's firing?
have you checked the pigtail this season?
is the water dirty in the sightglass?
does it bounce much?
post a general picture floor to ceiling showing the pipes also,
and one closer in of the Ptrol controls, sightglass,
Your pressuretrol settings may have no relation to real pressure in the system.—NBC
- Either the Pigtail, (the looped pipe that the Pressuretrol is mounted on) is clogged and the Pressuretrol can't manage the pressure. Or
- The boiler needs to be skimmed. Has any new piping or anything been added to the system since last season? It sounds like there is oil on the surface of the water, making it difficult for the steam bubbles to break through and that is pushing the boiler water back out through the return. Draining the water out of the boiler does not get rid of the oils. They just cling to the side walls when you drain the water out and resurface when you refill the boiler.
- Also, if you have the 404 Pressuretrol, (the gray box) set the cut-in to .5 or .75 and set the white wheel, inside the gray box to "1", facing the front of the box.