Only half of my Radiator heats up
mcp1
Member Posts: 86
I recently had one of my old cast iron steam radiators refinished. It was dipped in an acid bath, sand blasted, primed & painted; it looks great. When i hooked it back up, only 2 or 3 of the rails are heating up out of the 9 rails on the radiator. What would cause this? I'm not sure if there's a blockage or what. Hopefully someone has some suggestions on how to get the heat to the rest of the radiator.
Is there a working air vent on the radiator?0
Yes, I have a Danfoss thermostatic radiator vent on it. The vent is set at 4. The radiator is located on my 2nd floor and the riser only supplies this radiator.0
And did your refinishing and painting people leave the opening for the air vent open? Or paint it shut?Br. Jamie, osb
The opening for the air vent was open. I replaced the vent when i reinstalled the radiator.0
Just a vent? Or a Danfoss thermostatic radiator valve? And if the latter, to what do you have it set?Br. Jamie, osb
It's a Danfoss thermostatic radiator valve set at 4
OK -- then the question is, is the room getting to the temperature you want? If it is, the Danfoss is doing exactly what it's supposed to do: close the venting when the room is up to temperature. No need to have the radiator pumping out heat that you don't want...Br. Jamie, osb
Can we see a picture of the radiator showing both ends?0
I'm hearing at least two changes here. 1) the radiator was removed and refinished, which isn't likely to be the source of the problem or 2) the vent was replaced with a Danfoss thermostatic vent. Either that vent is working like it should (if the room is up to temp) or the setting needs to be increased or the vent isn't working at all and the steam is compressing the air in the radiator enough to allow 2 or 3 tubes to heat up. In any case, I think the issue is at the vent.
I suppose there is a third possibility, that the supply valve isn't fully open or when you did open it, the disc inside the supply valve came loose and isn't letting steam into the radiator.1 -
Thanks for the feedback guys. I'll put up a picture. Fred, how would i know if the Danfoss vent is working? I'm going to set the vent at 5 and see if that does anything. If the vent isn't working should i replace it with a varivalve vent?0
Don't replace it with the Varivent. They are so aggressive that they will spit water. You can use the Vent-Rite #1 or the Hoffman #1A. Both are adjustable.mcp1 said:Thanks for the feedback guys. I'll put up a picture. Fred, how would i know if the Danfoss vent is working? I'm going to set the vent at 5 and see if that does anything. If the vent isn't working should i replace it with a varivalve vent?
About the only way I know of to test the Danfoss is to take it off and use one of the two vents I suggested and see if that fixes the problem.1 -
You have to keep in mind that the TRV-air vent you have will only shut off the heat by preventing air venting, not call the boiler to come on for more heat. The boiler has to shut down for it to open and start over.
If you turn it up all the way does it heat more?0 -
Jughne, I turned up the vent and now I'm waiting to see if that works0
Jamie, when using the Danfoss vent the temp is not what i would like the room to be. I would like the room temp to be warmer.0
Turn it up. If your boiler cycles often enough, that will work (the boiler has to cycle off for the TRV to reset).mcp1 said:Jamie, when using the Danfoss vent the temp is not what i would like the room to be. I would like the room temp to be warmer.
I presume that you couldn't control the heat properly with a conventional vent?Br. Jamie, osb
I might add -- there is a common misconception with TRVs that if you turn it up you will get heat. Doesn't work that way. If you turn it up, it will let the radiator heat longer -- the next time the boiler turns on. Further, it is quite possible that the actual vent you have attached to the TRV is too small to let the radiator heat enough anyway.Br. Jamie, osb
You guys are a big help, thanks!!!0
- 125 Chimneys & Flues