Frozen Baseboard

Company moving to new building, but the heat has been off and nobody drained the system. The first floor baseboard was run through the concrete and I assume will be full of leaks. The second floor baseboards have blown out solder joints. (Not even mentiioning the bathroom water lines.)
The first question I have is it a problem to replace the first floor zone baseboards with two unit heaters? Basically just 2 open rooms.
Question 2- what are the chances the boiler is blown apart.? Have not had a chance to put some air pressure in it yet.

Comments

  • Steamhead
    Steamhead Member Posts: 17,376
    This is, to put it mildly, a can of worms.

    You'll need to pressurize every part of the system. I prefer to use water rather than air since leaks will be easier to see.

    What is the first-floor room used for, that you want to put unit heaters in?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    mattmia2
  • Jamie Hall
    Jamie Hall Member Posts: 24,839
    Yes, water. Not only is it easier to see, but if something breaks -- which in your case is likely, assuming you can get any pressure on it at all -- it won't go far. With even medium pressure air behind it, it would become shrapnel, which can ruin your whole day.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Got any pictures of 'blown out solder joints'? Never seen one, but I’ve seen plenty of copper split by freezing.

    There was an error rendering this rich post.

  • mattmia2
    mattmia2 Member Posts: 10,920
    I've seen a cap pushed right off the end of an air chamber.
  • JUGHNE
    JUGHNE Member Posts: 11,274
    Is it possible to isolate the boiler with valves to just check that out for leaks.?
  • hot_rod
    hot_rod Member Posts: 23,373
    tough call, if you test with water have some wet vacs ready to go. The water can add insult to injury.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    mattmia2fenkel
  • PerryHolzman
    PerryHolzman Member Posts: 234
    edited January 2021
    How is it that your company agreed to move into a building with a substantially damaged heating system. While it may be repairable - it will not be cheap; and you may need to replace the entire thing (and redo the walls and floors in the process).

    If I was planning on this I'd plan on a 100% new system and assume that nothing could be reused. Now maybe the radiators can be reused (if they did not crack). But a total solid freeze of the system indicates likely major replacement of the entire system.
    STEAM DOCTOR
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    Warm air system with AC?
    Rooftop units with single-floor buildings
    Just an economical thought, since we agree that the entire system may need to be replaced. Why spend any $ at all on the boiler?

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • garfieldsimons
    garfieldsimons Member Posts: 14
    Well now pretty sure there is a Big ice cube in water heater. Pulled it out (very heavy) and has been dripping all day. At that rate will be defrosted by March. No info yet on boiler.
    Unit heaters would be for 1k sq ft. area. Not offices.

    The building (steel frame-about 7k sq feet) was a good price and way cheaper in long run then the rent currently paid. Main area has gas radient heaters on ceiling. They should be fine. Base board heats only about 2- 1k sq. ft. floors.

    Business is holding on by shoe string; a very worn shoe string. Sheet metal shop making percusion musical instruments. Every dime matters now.

    Thanks for all your inputs.

    BillyO
  • mattmia2
    mattmia2 Member Posts: 10,920
    If the boiler or a significant part of the piping is trashed you could just hang a couple gas direct vent unit heaters.