Can I bypass this ventless radiator in the basement?

There is a very strange radiator in my basement. The upper right of the radiator connects to a supply. Just inside the wall, the lower left rejoins the dry return below the radiator. There is no vent. There is no valve. The radiator rarely gets more than a little bit warm. It is a one-pipe system.

I posted about this radiator about a year ago. The thought was that this was a "condensate heater," possibly put there to satisfy draft requirements back when the house was built in the 1920s.
(That earlier conversation then went off the rails about my ceiling joists. To reiterate: they're fine. The notches are 80 years old. I only found out about them because I took down the ceiling, as we had never had a problem with them. I consulted two structural engineers proactively as soon as I saw the notched joists. Both engineers said to sister the joists and move on, and one recommended the carpenter that did the project.)
My question is: can I safely have this radiator removed from the system entirely? If so, can I simply cap the pipes at the upper left and lower right, or should I still have a pipe that connects them? If I need to connect them, does it need to cut diagonally across the opening, or can it make a right angle? I'd love to reclaim this precious wall space for a mini-split and/or a HRV.

I posted about this radiator about a year ago. The thought was that this was a "condensate heater," possibly put there to satisfy draft requirements back when the house was built in the 1920s.
(That earlier conversation then went off the rails about my ceiling joists. To reiterate: they're fine. The notches are 80 years old. I only found out about them because I took down the ceiling, as we had never had a problem with them. I consulted two structural engineers proactively as soon as I saw the notched joists. Both engineers said to sister the joists and move on, and one recommended the carpenter that did the project.)
My question is: can I safely have this radiator removed from the system entirely? If so, can I simply cap the pipes at the upper left and lower right, or should I still have a pipe that connects them? If I need to connect them, does it need to cut diagonally across the opening, or can it make a right angle? I'd love to reclaim this precious wall space for a mini-split and/or a HRV.
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 129 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 560 Plumbing
- 4.2K Radiant Heating
- 332 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
On cutting it out. That depends on what it is doing (or not doing) rather than why it is there at all. There are three things it might be doing: helping to vent the steam main which feeds it; helping (oddly) to vent the dry return into which it connects; and providing some heat to the space. There is also a chance that it actually also serves as a drip of sorts for the steam main.
So... it's not providing much heat, and you don't need the heat anyway. So much for that one.
Now. Venting. If the steam main to which it connects is adequately vented, while it may be vaguely usedful for that it would seem it isn't required. Had this been a situation where the main was not vented, but the dry return was, then it would have been needed -- and the condensing capacity would have made moderately certain that steam would not get into the return and mess things up. So this option must be considered, but, as I say, if the main is otherwise adequately vented, can probably be discounted.
On the other hand, there is the question of the return -- and there one has to ask how that return is vented. If it is a true dry return (oh dear, here we go again!) -- that is, separated from the steam mains by a trap and possibly a water seal, and accepting air released from radiators -- then the return does need to be vented somehow (usually with a vent or cluster of vents at the boiler). On the other hand, if the return is simply an extension of a steam main, then it is not surprising it doesn't heat -- more or less equal pressure on both sides -- and isn't needed for venting, as the steam main vents do that.
I think on the whole the possibility of its serving as a combination drip and vent for the steam main is actually pretty good, particularly if that dry return is a true dry return.
I would really have to look at how the rest of the system involving that main and return is piped to be sure, but on the whole I would think that if there is adequate venting for those pipes, and if there is a definite way for condensate in the steam main to make its way back to the boiler somewhere else, it could probably be simply capped at both inlet and outlet and filed under "hmm... I wonder what that really was for?".
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
Is the inlet the end of the steam main?
Where is the air venting for the system.
Is the lower pipe truly a dry return?
We have never seen the entire piping system because part of it is in the wall., including a piece that is sandwiched between brickwork and a beam where there had been an extension built 80 years ago. When we had the ceiling open, though, we saw the connection from the main to the inlet, and we can see where the radiator joins the return below on the left, just inside the wall.
The kitchen floor is so well heated above my boiler room I’ve debated if I could remove that radiator at some point as I consider renovations. Maybe add a couple small sections of steel fin tube off the dry return and drip them back to the boiler return if needed.
Are there any unions close to the rad? I don't see any.
At the end of the steam main where the air vent is located, is there a return line connected on the end of the main?
Was the inlet to this connected to the bottom of the main?
If so and there is no end of main return, this section of main could have been counter flow and the rad is the drip for returning condensate.
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating
Also, think about where the water line was on the original coal boiler, usually they were much higher than on a modern boiler.