Primary/Secondary mod con boiler issues
Jeff_Suda
Member Posts: 3
I just installed a lochinvar nobel 199 combi boiler we a primary/secondary configuration with 5 zones. While tuning the ODR I was getting system water temps that don't make since to me so though someone here might know what's up.
The issue I'm seeing is my boiler outlet temp is 177, my inlet temp is 169 (primary loop), my secondary manifold supply temp is 157 (system temp), and my secondary monidold return temp is around 151.
The issue I'm having understanding is how is this possible. If I'm over pumping on the primary side you would expect to see the secondary manifold supply temp the same as the boiler outlet temp. If I'm over pumping on the secondary loop you would expect to see the boiler inlet the same as the boiler manifold return. Can someone explain what's happening?!
for the boiler inlet and outlet Im getting that from the boiler control panel, for the secondary loop manifold I'm getting that from a boiler supply temp & a mechanical t&p gauge, and for the secondary loop manifold return I'm getting that from only a mechanical T&P gauge.
Lastly let me know if you see any glaring issue with my install. I realized I didn't level 12" above the zone circulators as dictated by taco so I will be fixing that on a warm day by dropping the mainfold down a little. Also the 5th zone is not hooked up yet as that will be a future garage as and I haven't hooked up the condensate neutralizing piping.
The boiler is running and heating but I just can't make since of the #s
The issue I'm seeing is my boiler outlet temp is 177, my inlet temp is 169 (primary loop), my secondary manifold supply temp is 157 (system temp), and my secondary monidold return temp is around 151.
The issue I'm having understanding is how is this possible. If I'm over pumping on the primary side you would expect to see the secondary manifold supply temp the same as the boiler outlet temp. If I'm over pumping on the secondary loop you would expect to see the boiler inlet the same as the boiler manifold return. Can someone explain what's happening?!
for the boiler inlet and outlet Im getting that from the boiler control panel, for the secondary loop manifold I'm getting that from a boiler supply temp & a mechanical t&p gauge, and for the secondary loop manifold return I'm getting that from only a mechanical T&P gauge.
Lastly let me know if you see any glaring issue with my install. I realized I didn't level 12" above the zone circulators as dictated by taco so I will be fixing that on a warm day by dropping the mainfold down a little. Also the 5th zone is not hooked up yet as that will be a future garage as and I haven't hooked up the condensate neutralizing piping.
The boiler is running and heating but I just can't make since of the #s
0
Comments
-
-
What type of heat emitters? that you are running the boiler that hot.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes, the boiler loop is piped backwards and if you simply flip the pumps then the secondary will be backwards and you'll be pumping toward the expansion tank. Just fix it right and switch the boiler piping around0
-
Lots of nice pro press scrap copper too bad.
Everyone occasionally pipes something wrong occasionally. I had a guy helping me pipe a warm air gas furnace . I was doing the gas and he was doing the pvc flue and intake.
he had the flue on the left and intake on the right in the basement. He went outside and put the terminations on the wrong pipe.
0 -
The temperature to the zone circulators will change based in the gpm, or how many circulators are running.
Assume the boiler has a single speed, non variable circulator 15 gpm flow perhaps?
If one 2 gpm circ is running the mixed temperature will be different compared to when 4 circs are running, may be an 8 gpm load.
With some data or assumptions you can calculate or predict what the temperatures will be. Usually one side has a larger flow rate, on some occasions the boiler flow and the distribution match exactly, then there is no mixing and expect to dee boiler outlet temperature at the distribution.
Are you using the boiler supply sensor to maintain a temperature to the secondary loop? the boiler can modulkate attempting to maintain a "target" SWT.
I think you have what is referred to as reverse injection, which can work if you have the flow rate required. Tekmar has a good explanation, shown in their essay sheet attached. See by their formulas and the color and size of the flow arrows what is going on with the direct or reverse injection.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
@hot_rod baseboard fin tube but that was only temporary until trying to get it to work. Now that the flow direction is correct the temps are way down
@GroundUp thanks for the incite. I'm definitely going to fix it but with news years unfortunately my plumbing supply is closed until the 4th and I need some new unions and primary/secondary tee. Unfortunately flipping the pumps is what I have to do for a few days.
@EBEBRATT-Ed the one downside of pro-press...when u screw up u waste a ton of fittings... Luckily it looks like I can just have the primary loop cross itself so I only have to scrap the unions, tee and a few elbows... Most everything else hopefully can stay the same.... I still can believe I did this0 -
can we see a picture of the fix under the boiler,
please?known to beat dead horses0 -
the right side tapping of the boiler is the CH outlet?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements