Taco ZVC404-4 and C Wire with Digital TStat
Majortomm
Member Posts: 1
I have a Taco ZVC404-4 that was installed last year connected to my boiler for heat in 3 zones. Zone 1 upstairs heat, Zone 2 downstairs heat and Zone 4 (priority) for sidearm hot water heater.
The current Tstats are wired R & W only with the C on the Taco not used. I recently purchased a smart thermostat (Wyze) to test out and I have connected it to my upstairs Zone 1.
The Blue and Green wires running to the Tstats are not connected so I connected the Blue to the C on the Taco controller for Zone 1. I then wired everything to the thermostat as instructed: R to Rh, W to W1, and C to C. When I connect the smart thermostat it doesn't power up at all. When I connect the old honeywell Tstat everything works (battery powered) and triggers the zone controls as expected.
Am I missing something? Is there anything I need to do on the Taco board to enable the C? What are some troubleshooting steps I should be trying to eliminate any possible issues before I declared the new smart Tstat "dead on arrival"?
The current Tstats are wired R & W only with the C on the Taco not used. I recently purchased a smart thermostat (Wyze) to test out and I have connected it to my upstairs Zone 1.
The Blue and Green wires running to the Tstats are not connected so I connected the Blue to the C on the Taco controller for Zone 1. I then wired everything to the thermostat as instructed: R to Rh, W to W1, and C to C. When I connect the smart thermostat it doesn't power up at all. When I connect the old honeywell Tstat everything works (battery powered) and triggers the zone controls as expected.
Am I missing something? Is there anything I need to do on the Taco board to enable the C? What are some troubleshooting steps I should be trying to eliminate any possible issues before I declared the new smart Tstat "dead on arrival"?
0
Comments
-
-
Try using the Green wire for common. Also be sure the TACO 404-4 thermostat wire is connected properly. On a 2 wire thermostat setup, you can reverse the R and the W at the thermostat or the control without any problem. When you use a common... You must wire R on the control the Rh on the thermostat. So look inside the Taco Control and the thermostat to see that the wires are not crossed.
Taco Thermostat
..R.............Rh
.W.............W
..C...............C
Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics1 -
Do you need to jumper the R & Rh terminals in the thermostat?0
-
That depends on the inner workings of the thermostat. Some must have power to R or Rc for the thermostat microprocessor to operate. Then the answer would be YES .MikefromMn said:Do you need to jumper the R & Rh terminals in the thermostat?
I'm not familiar with Wyze thermostats. The original post does not indicate that to be the case. You do bring up a good point though. Something to look at if the system fails to operate with Rh only.Edward F Young. Retired HVAC ContractorSpecialized in Residential Oil Burner and Hydronics0 -
If you have no cooling equipment, the jumper can remain or be removed.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hourTwo btu/ per sq ft for degree difference for a slab0
-
Have you programed the thermostate correctly?0
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 768 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements