climatmaster21 water to air
Options
george_42
Posts: 123
What air temps should I be getting on heat cycle,( outside air 25 deg,) out of plenum. I get about 90 deg
0
Comments
-
The manuals get into the engineering and temp rise numbers but 90 is a good average Heat Pump air temp. Mentioning the room temp helps the opinions too0
-
thank you, I was just wondering if I was in range0
-
25-30f temp rise is about right for any heat pump at nominal conditions.This is a geothermal unit, outside air temp is irrelevant. Entering water temp and delta T are what matters. Then you can check approach temps if needed.0
-
ah yes getting more technical Moto. Presumably, colder outdoor temps would also cool off the loop though; have an affect on air temp (we don’t know if it’s open or closed loop)0
-
Cooler temps might cool a slinky horizontal loop a little. But a normal horizontal bored loop is too deep a vertical is way too deep. Ground
conduction and total heat loss and gain vs installed ground loop capacity will determine how much it swings.0
Categories
- All Categories
- 87.9K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 60 Biomass
- 430 Carbon Monoxide Awareness
- 133 Chimneys & Flues
- 2.2K Domestic Hot Water
- 6K Gas Heating
- 124 Geothermal
- 170 Indoor-Air Quality
- 3.9K Oil Heating
- 80 Pipe Deterioration
- 1.1K Plumbing
- 6.7K Radiant Heating
- 397 Solar
- 16.1K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements