Banging pipes at specific times

JodiMe
JodiMe Member Posts: 74
Hi. My pipes and system are generally very quiet but occasionally in the morning, when coming up to day time temp, we get some major banging in them.

A bit before we usually get out of bed, we set it from overnight temp (66) to 68 so we can muster the strength to get out of our warm covers. Then an hour later, as we are getting up and at em, we have it go up to 69. The banging almost always seems to happen just as we start that second cycle. 

Anyone know why this could be? It doesn’t seem to happen at any other time.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,973
    hot water? Steam?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JodiMe
    JodiMe Member Posts: 74
    Steam
  • Jamie Hall
    Jamie Hall Member Posts: 23,973
    The long run from 66 to 68 is producing a lot of condensate -- and somewhere... hard to say where... some of it is hanging up long enough so that when the heat comes back on, it bangs. Question is... where?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JodiMe
    JodiMe Member Posts: 74
    That makes sense. Maybe we will play with the timing settings a little and see if we can get in the sweet spot where it doesn’t happen. It’s not every morning but even once in a while it’s concerning/annoying.
  • bburd
    bburd Member Posts: 954
    First, figure out where the banging is coming from. Then check pipe pitch to ensure that condensate can drain freely. 

    If you have fast radiator vents in that part of the system, slowing them down will reduce the rate of condensate generation.

    Bburd
    JodiMe
  • Fred
    Fred Member Posts: 8,542
    Look for a pipe or pipes that have lost their pitch or have a sag in them and correct the pitch or sag. If the banging sounds like it is coming from under a floor board, near a radiator, try to raise that end of the radiator to get the pitch back, in the pipe under the floor board, and then re-pitch the radiator.
    JodiMe
  • JodiMe
    JodiMe Member Posts: 74
    Thanks for the help. I know exactly where it’s coming from so I’ll take a look. We do have a fast vent on that specific radiator since it’s at the opposite and of the house from the boiler and is pretty sizable. 
  • bburd
    bburd Member Posts: 954
    Also be sure the radiator shutoff valve is fully open.

    Sometimes the valve disc becomes detached from the stem; then the steam and condensate fight each other and can produce gurgling and/or water hammer.

    Bburd
    Dave T_2
  • JodiMe
    JodiMe Member Posts: 74
    How do I check this? 
  • JodiMe
    JodiMe Member Posts: 74
    Oh, never mind. I’m slow on the uptake today! I’ll double check those...