Help!! Regulator problem or bad gas?

Options
MnBen
MnBen Member Posts: 2
Same tank... two furnaces, one in the garage and one in the house. Both started short cycling at the same time. The gas company replaced the high pressure regulator at the tank...did not fix the issue. 

When there is a call for heat in the house pressure drops “significantly” at the low pressure regulator on the house, the furnace inside (York diamond 80) ignites until the blower kicks in and then loses flame... 

Garage: the big max mr heater (brand new and was converted to propane) ran great until it didn’t!. It continues to short cycle but runs a few minutes before dying. 

This is way to coincidental... 

Comments

  • rick in Alaska
    rick in Alaska Member Posts: 1,457
    Options
    The only way to tell would be to put a pressure gauge on the line before the low pressure regulator, and one after it and see how they respond when you run anything. The pressure shouldn't drop much. Could be the low pressure regulator is defective.
    Rick
  • Zman
    Zman Member Posts: 7,569
    Options
    Is this a new construction?
    What are the BTU ratings on the appliances.
    Most buildings with a significant load have a regulator at the tank and and regulator at the building. This is to eliminate the pressure drop issue in the smaller underground line.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • MnBen
    MnBen Member Posts: 2
    Options
    Not new construction... house was built in 1900 but the garage was just redone. Both structures have a low pressure regulator at the house. 80k 
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Options
    Ok, so you have one first stage regualtor at the tank and that serves two second stage regulators? One for that garage and one for the house? 

    Are there two pipes coming out of the first stage reg at the tank? 
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,549
    Options
    You need to check piping and regulator sizing. Also the size of the tank is important. A small tank in cold temps will not vaporize enough gas to keep up. It can freeze up regulators