W/M Aquabalance WMB120 combi A02 code-False flame indication, HELP
andymar
Member Posts: 25
in Gas Heating
My gas Weil McLain Aquabalance 120 WMB120 combi is two years old. I have been getting an A02 false flame indication error code with a hard lock out. I initially cleaned and re-installed the ignitor electrode. Problem continued. I replaced the part and again the problem persists. After re-setting the unit will operated both DHW and heat for 12 to 24 hours, cycling on and off, then go into A02 mode. Please help.
0
Comments
-
It's not the ignitor. The cad cell is probably seeing light when it shouldn't -- or is defective of misadjusted.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank you for your response. I do not see a cad cell listed on any diagrams in my manual. Is it possible the cell is included in any other part? Is this something that can replaced as a homeowner without specialized tooling or gauges?0
-
There isn't one on gas units,only oilandymar said:Thank you for your response. I do not see a cad cell listed on any diagrams in my manual. Is it possible the cell is included in any other part? Is this something that can replaced as a homeowner without specialized tooling or gauges?
To learn more about this professional, click here to visit their ad in Find A Contractor.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements