Welcome! Here are the website rules, as well as some tips for using this forum.

Need to contact us? Visit https://heatinghelp.com/contact-us/.

Click here to Find a Contractor in your area.

If our community has helped you, please consider making a contribution to support this website. Thanks!

LAARS MASCOT FT 140 k model

Options
I have 2 units of the mascot ft 140k boilers ( side by side). I have an issue with heat for one unit. 
The domestic hot water DHW works fine, however there is no heat. When you call for heat the unit turns on and you can see the flame inside the exchanger, however there is no circulating hot water. 
I had this issue last year with the other unit and it was the 3 way valve. However last year the unit displayed an error msg, which isn’t the case this time. 
There is only one zone on this unit supplied by a webstone circulating pump. The pump seems to work when compared the to the other unit. 
I included some pictures below. 
Couple additional info, The baseboard doesn’t have any relief valves, could air in the system cause this. 
Could the 3 way valve be the issue even though no error msg, or even the unit internal pump.
any help will be appreciated. Thanks


W 

Comments

  • Ironman
    Ironman Posts: 7,975
    I was working on the exact same model boiler yesterday.

    You need to confirm whether or not you have flow in the house loop before assuming that the 3 way valve is bad.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Mez
    Mez Posts: 10
    And how can you do that. I checked the  circulating pump electrical and it get power when I call for heat. 
  • Ironman
    Ironman Posts: 7,975
    edited December 2020
    With a heat call, feel the temp of the system supply and return lines a few feet past the boiler. There should be about 15-20* difference after it's been on for a while.

    Then feel the supply and return coming out of the bottom of the boiler before the manifold. They should be about the same as the system lines. If they are extremely hot, and the system lines are substantially cooler, then you don't have circulation on the system side.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Mez
    Mez Posts: 10
    Thanks bob for getting back to me. So I had the unit running for 15 min. Pic 1
    The pipes inside the unit are hot, the pump is hot too.  Pic 2
    However the outside piping is cold 56deg ( basement temp) pic 3


  • GroundUp
    GroundUp Posts: 2,573
    If the DHW function is working, the internal circ is flowing water. This is a very common issue with these, the 3 way is stuck. They don't always throw an error code
  • Mez
    Mez Posts: 10
    Thank you very much for the reply Groundup. It seams like it’s the 3way valve. 
    I purged the lines, I descaled the exchanger. I also checked the zone circulating pump and it seams to work. I will give the 3 way valve a try
  • Ironman
    Ironman Posts: 7,975
    If the pipes between the the bottom of the boiler and the manifold are both hot, then its not the 3 way valve, its a SYSTEM circulation problem.

    There's also a strainer at the pump inlet on the bottom of the boiler. Caution: you have to valve off the boiler and depressurized it first.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Mez
    Mez Posts: 10
    Thank you guys for the insights. I ended up replacing the 3way valve, and it’s working good. Now the zone pipes and heaters are hot, a Temperature are about 112 to 95 ( in - out). 
    If someone this issue in the future there is a good video on YouTube
     https://youtu.be/9eJdG3bG84k 
    Or you can just type laars mascot 3way and come right up. 
    For those who took time to provide their expertise, thank you very much. 

    his
  • BillyO
    BillyO Posts: 277
    Ken Resnick is the Babe Ruth of Laars service, I am naming my next child after him!!!
    Le JohnPeteA
  • GroundUp
    GroundUp Posts: 2,573
    Ironman said:

    If the pipes between the the bottom of the boiler and the manifold are both hot, then its not the 3 way valve, its a SYSTEM circulation problem.

    There's also a strainer at the pump inlet on the bottom of the boiler. Caution: you have to valve off the boiler and depressurized it first.

    The piping between the boiler and the purge tee was cold
  • Ironman
    Ironman Posts: 7,975
    All that rust is not a good indication. It's probably the cause of the failure.

    That system needs to be properly flushed and cleaned and a dirt mag installed on the return. Also, any leaks need to be located and repaired.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    fenkelGroundUp
  • Mez
    Mez Posts: 10
    edited December 2020
    Bon,
    i did flush both the heating and the DHW loops using city water, is there some kind of liquid that can be Introduced into the system to clean the inside pipes?
    i already descaled the exchanger
  • BillyO
    BillyO Posts: 277
    HTP and Laars same problem. Changed 6 3way valves in last 3 years. Horrible engineering
    SuperTechfenkel
  • Ironman
    Ironman Posts: 7,975
    Fernox boiler cleaner + a dirt separator on the return.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    fenkelMez
  • Ironman
    Ironman Posts: 7,975
    All that rust indicates oxygenated water. That mean there’s a leak(s) that needs to be fixed.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    fenkel
  • Le John
    Le John Posts: 250
    I’m wondering why more manufactures don’t use the Caleffi made three way valve that is in the Lochinvar Noble combi.  
  • Le John
    Le John Posts: 250
    BillyO said:
    Ken Resnick is the Babe Ruth of Laars service, I am naming my next child after him!!!

    @BillyO Ken and Rathe Associates is a great representation of a boiler rep that knows the Laars boilers and helps its customers with questions or problems whenever and however they can.

    BillyO
  • EzzyT
    EzzyT Posts: 1,380
    This is one of the reasons why we shy away from wall hung combi units. To much reliance on poorly manufactured components to operate once heating or cooling equipment.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    fenkel
  • Mez
    Mez Posts: 10
    edited December 2020
    The cost of the 3 way valve is around $80, and it’s covered by the warranty. Actual replacement $, out of pocket. Go figure! These manufacturers come up with crappy products and hide behind their warranty. 
  • PeteA
    PeteA Posts: 328
    I know this is a few years old but I’m considering one of these and I’m curious these still experiencing similar failure points in the 3way valve like some of the other posters say? I love the idea that it seems like it’s easy to work on and parts are available and normal O rings everywhere 
  • hot_rod
    hot_rod Posts: 28,705
    Looking at the water in the bucket and the rust build up inside the valve body, that is not a manufactures defect. A squirt of conditioner in every boiler you install could prevent most of these type of failures.
    Assuming the system is leak-free
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    PeteAGGross
  • I was having the same issue and couldn’t believe the 3way was faulty so I dug deep on this and found micro switches under the cover, one had failed, carbon on the contacts, was able to clean up and get it going. Couple bucks on Amazon if you’re so inclined. PN KW4A(S). They’re plastic welded onto a couple pins and I got lucky they popped right out.

    IMG_8888.jpeg IMG_8886.jpeg


    Found two part numbers for the 3way ft1220 and ft2071, maybe the new one is improved.
    Anyway mines all rusty inside but that wouldn’t cause the micro switch to fail… I’ll try the conditioner as suggested.
    hope that helps

  • Wanted to add that I had no error codes. Symptom was hot dhw but no zone heating. This was caused by the blue wire switch failure and can be tested with a continuity test between the blue wire (follow wire up to a blue, red, black connector on the main board) and the double black wires on the actuator motor. They are normally closed switches so blue circuit should have continuity in dhw mode and red circuit should have continuity in ch mode.

  • psb75
    psb75 Posts: 1,181

    Good work everyone! Nice sleuthing and solving.

  • psb75
    psb75 Posts: 1,181

    Short, succinct discussion. Good pics. Very helpful to all.