Munchkin T40M rumbles and vibrates when firing from low temp
nbereny
Member Posts: 1
First time poster here, homeowner. CA, Bay Area.
Had the T40M Munchkin Boiler installed about 10 years ago to support radiant heating. It seems to definitely be struggling lately to hold temps when the temp drops outside to <40.
Recently, it has started rumbling and vibrating when it fires up at low temps.
The two use cases are:
1. Temperature on the boiler is around 70-90 in the early afternoon when the outside temperature is warmer. When the boiler fires up at this temperature late at night, it starts rumbling each time the boiler fires. And this goes on every minute or so, and can sometimes go for over an hour. When the temp reaches about 120, further firing does not seem to make the unit rumble. The sound is like a large truck stalling.
2. It seems to especially also happen when the temperature dips to <40. Not often in CA, but it still does. When the temp is around 40 +, the system does not seem to rumble.
The tech from the company who installed it came out and could not reproduce it because he comes in the morning when the temps are at 125 or 128. Turning unit on/off etc does not reproduce it.
Can this be fixed? Or is it time to replace the munchkin? I also reached out to HTP with this issue.
Help!
Had the T40M Munchkin Boiler installed about 10 years ago to support radiant heating. It seems to definitely be struggling lately to hold temps when the temp drops outside to <40.
Recently, it has started rumbling and vibrating when it fires up at low temps.
The two use cases are:
1. Temperature on the boiler is around 70-90 in the early afternoon when the outside temperature is warmer. When the boiler fires up at this temperature late at night, it starts rumbling each time the boiler fires. And this goes on every minute or so, and can sometimes go for over an hour. When the temp reaches about 120, further firing does not seem to make the unit rumble. The sound is like a large truck stalling.
2. It seems to especially also happen when the temperature dips to <40. Not often in CA, but it still does. When the temp is around 40 +, the system does not seem to rumble.
The tech from the company who installed it came out and could not reproduce it because he comes in the morning when the temps are at 125 or 128. Turning unit on/off etc does not reproduce it.
Can this be fixed? Or is it time to replace the munchkin? I also reached out to HTP with this issue.
Help!
0
Comments
-
Have you checked the fan assemble? Its made up with plastic and can wear out and wobble on start ups.
Any codes?0 -
-
Zman said:When is the last time it was disassembled and cleaned? Has a combustion analysis been performed recently? Munchies are great little boilers, they need regular serving.
0 -
-
Did HTP make a T40M? What is the nameplate model #.
It's a combustion issue as Zman suggests. Clean it and do a combustion analysis on it with a recently calibrated CO meter.0 -
The rumbling sounds as though the gas/air mix is too rich and needs to be adjusted by someone that has a manometer.
I'm in Berkeley if you want to talk about it. (510)773-9870 cell
Munchkin boiler sizes are T50M, T80M, T140M and T199M.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I dug out an old manual and all I see is a T50M and a T80M.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements