Water heater sooting
kcopp
Member Posts: 4,472
in Gas Heating
18 month ol WH Install. LP Gas. Natural draft. Unit shut down... fortunately. What are some reasons for this sooting???
0
Comments
-
What were the combustion test results? The only way I can think of to get that catastrophe is the air/fuel ratio being way off.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Burning on the bottom side of the burner? (leaking gas)
Gas valve not shutting off 100%?
Low gas pressure?
Air inlet screen/grid plugged?0 -
Hi, It could be something is interfering with air flow, either out or in. Also, you’ll want to clean the flue baffle of all the soot it’s collecred
Yours, Larry0 -
Is it an LP water heater?0
-
Unit does not work now....So I cant test combustion. Yes propane.
Plenty of air flow. Sits up on bricks...no blockages.
Vent up top looks clean.
I not even sure I want to clean up... I think it would need a whole new burner and pilot assembly.
0 -
-
I think what @realliveplumber meant is. Is the heater actually made for LPG. We understand it's running on it.
What I do know is I don't want that in my house. For LP and NG to soot something is really really wrong.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
NG burner running on LP?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
I agree that is a VERY good question.neilc said:why is that lint screen all corroded away in that middle picture ?
In my view, the most likely reason for this sooting condition is that the combustion air going into the burner compartment has been obstructed.
0 -
All good questions...
The screen looked melted.
The heater is labeled for LP gas.
Would an undersized gas line cause this?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements