Hot Water Baseboard Zone Hot without Calling for Heat

Options
razzor
razzor Member Posts: 20
Hi,

I had a new Biasi boiler put in a year ago, replacing a leaking Burnham V75 or 71. In the last year I have not saved a penny in oil and I have the baseboard zone for my main house getting hot even though the thermostat for that zone isn’t even calling for heat. I don’t think I have zone valves, just circulator pumps. The circulators are on the return side. Does anyone know what could be causing this? I thought I would be saving with oil consumption with this new system. I have enclosed pictures and highlighted the zone that is the issue.

Thanks.






Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,338
    Options
    First place, on energy saving: unless the new boiler has a significantly higher efficiency than the old one, and -- if it is a modulating boiler -- is run to take advantage of that higher efficiency, there's no reason to suppose you would save any energy: a BTU is a BTU, and it takes a certain number of BTUs to heat the structure. The Biasi boiler is excellent -- but it is not a mod/con, and unless it was tuned nearly perfectly, it isn't enough more efficient than the Burnham it replaced to make a noticeable difference.

    Sorry about that. Physics is a rather unforgiving science.

    Now on the zones heating when you don't have their specific pumps running -- that's common enough, and is referred to as ghost flow. The best and often only cure is check valves on the zones.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited December 2020
    Options
    @Jamie Hall He has flow cheks.

    Flow check probably needs to be cleaned out or replaced.
    Oversized boilers don't save any money, which is what I guess you have with all those zones.
    I hope you got a great price on that install, because it looks like a swap out, virtually no new near boiler piping or anything corrected.

    OP, what did your contractor say when you posed the questions to them?

    There was an error rendering this rich post.

  • Jamie Hall
    Jamie Hall Member Posts: 23,338
    Options

    @Jamie Hall He has flow cheks.
    OP, what did your contractor say when you posed the questions to them?

    Didn't notice that. Sorry.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    STEVEusaPA
  • razzor
    razzor Member Posts: 20
    Options
    Steve, it was a swap out. All I could afford at that time. Are the flow checks the other items in my photo that aren’t the circulators?
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    Yes, the middle picture. They are all on the supply.
    When any other zone is calling, does it feel equally hot on both sides of that flow check? Same for its corresponding circulator.

    There was an error rendering this rich post.

  • razzor
    razzor Member Posts: 20
    Options
    Are the flow checks separate or are they part of the Taco circulator?
  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    Most flow checks have a manual bypass to open them by hand.
    Probably the nut on the top. It might be too crusty to move easily.
    If the flapper is stuck open you might convince it to close with a rubber hammer.
    Or remove the 3/4" square head plug to inspect.
    That would require draining the water.
  • dopey27177
    dopey27177 Member Posts: 887
    Options
    The best way to eliminate water creep is to install check valves after the pumps. The check valves will prevent water from being forced up the zone that is of line.

    Jake
    fenkel
  • razzor
    razzor Member Posts: 20
    Options
    Would it be the flowcheck or the Taco circulator that is allowing the water creep? The circulator is pulling through on the return side. Thanks. 





  • Jellis
    Jellis Member Posts: 228
    Options
    Hey @razzor
    the Universal Flow check is what should stop your zone from heating when its not calling.
    there is a flapper inside the valve that "swings" closed when the pump shuts off, stopping water from running through the pipes. When the pump kicks on it pulls the flap open and hot water flows through the zone.
    Sometimes these checks get stuck open causing the issue you describe.

    as described above you may be able to "exercise" the valve by opening and closing it with the nut on top. sometimes a love tap with a mallet is in store to get it to close fully.

    If I had done the boiler swap out for you I would have encouraged you to upgrade to new ECM circulators with built in checks and have done away with the old swing checks. those old checks may work fine for another 50 years... or they could start failing one by one... starting now