Pump coupler caught on fire
ddyckmam3
Member Posts: 1
in Oil Heating
The pump coupler on my Beckett AFG burner caught on fire today . Any ideas what might have caused this ? It melted the CAD eye as well .
0
Comments
-
Exhaust fan in the room? Power vent? Direct vent?
Seen them melt when pulling air down the chimney0 -
Pump free to rotate?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Back pressure. Plugged heat exchanger, blocked chimney, and/or negative room pressure pulling products of combustion backwards thru the burner.
Also incorrect burner set up, and on furnaces, cracked heat exchanger, clogged filter with an open return.
Figure it out before you fire it back up.There was an error rendering this rich post.
0 -
STEVEusaPA said:Back pressure. Plugged heat exchanger, blocked chimney, and/or negative room pressure pulling products of combustion backwards thru the burner. Also incorrect burner set up, and on furnaces, cracked heat exchanger, clogged filter with an open return. Figure it out before you fire it back up.
You have major problems. The burner is not safe to operate until the cause is identified and corrected. Call a pro who is familiar with oil heating systems.0 -
This.SuperTech said:You have major problems. The burner is not safe to operate until the cause is identified and corrected. Call a pro who is familiar with oil heating systems.
@ddyckmam3 , where are you located?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
It is a furnace if so did the air handler door fall off or did you change the filter? If it runs without the door it will pull negative pressure and suck the flame out the burner. Also everything else everyone has said.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements